Search the forum,

Discuss Can an EICR be unsatisfactory with only C3 codes? in the UK Electrical Forum area at ElectriciansForums.net

nrbham

DIY
Reaction score
4
I recently had and EICR done and received an 'unsatisfactory' report due to not all circuits being RCD protected on the consumer unit. The consumer unit was installed in 2007 and complied with all wiring regulations at the time (image attached). Does it need to be upgraded? I have attached the EICR with personal details removed. The EICR was done for a property which is due to be rented out.
 

Attachments

  • 0001.jpg
    378.1 KB · Views: 99
  • 0002.jpg
    412.8 KB · Views: 90
  • 0003.jpg
    431 KB · Views: 83
  • 0004.jpg
    542.1 KB · Views: 74
  • 0005.jpg
    497.5 KB · Views: 84
  • 0006.jpg
    514.7 KB · Views: 91
  • consumer unit.jpg
    371.4 KB · Views: 101
Last edited:
I'd get in touch with the person who did that report, say you've taken advice, and
1) you can't have an unsatisfactory report with only C3's
2) the two C3's don't stack up anyway, RCD protection is not needed for fault protection as disconnection times are met on all circuits, and RCD protection is not needed for fire protection as it isn't a farm.
If they don't apologise for their mistake and issue a satisfactory one, then plan B would be to get a letter saying all (fabricated) remedial work has been carried out and the installation is now satisfactory. Any competent sparks could have a look and do that for you, and this meets the PRS scheme obligations.

What's the first half of the postcode? Someone might offer to help you.
 
One of the main things he needed to fill in was serial numbers of test equipment, and he hasn’t even done that.

No tester name until circuit details, (which should have been redacted anyway)

Did you receive the last page? It explains when that unsatisfactory result only with C1 or C2.

I think they’re just looking for work by inventing problems.
 
One of the main things he needed to fill in was serial numbers of test equipment, and he hasn’t even done that.

No tester name until circuit details, (which should have been redacted anyway)

Did you receive the last page? It explains when that unsatisfactory result only with C1 or C2.
I assume the op has removed that information as he has done a good job in removing all location and inspectors details.
 
I'd get in touch with the person who did that report, say you've taken advice, and
1) you can't have an unsatisfactory report with only C3's
2) the two C3's don't stack up anyway, RCD protection is not needed for fault protection as disconnection times are met on all circuits, and RCD protection is not needed for fire protection as it isn't a farm.
If they don't apologise for their mistake and issue a satisfactory one, then plan B would be to get a letter saying all (fabricated) remedial work has been carried out and the installation is now satisfactory. Any competent sparks could have a look and do that for you, and this meets the PRS scheme obligations.

What's the first half of the postcode? Someone might offer to help you.
Spot on.

The inspector has managed so many important errors on this report it is fundamentally flawed.

A 0.06 ohm Ze would give over 3kA not 2.75kA

Since Zs = R1 + R2 + Ze I am not sure how he managed to get Zs to have lower values than R1 + R2 by a good margin!

He has also used the wrong values for maximum allowed Zs for the protective devices

I also find it difficult to believe he removed all the lamps etc in order to test between L-N and get 199Mohm


The fact that he shows RCD for additional protection as ok, when it's not there for all circuits, (yet not there for when it's not required) and doesn't appear to understand what he has measured or what it means, shows a fundamental lack of key knowledge that is required in order to undertake these sort of inspections.

If I was to believe the actual measured results, (and subject to not having done a visual assessment) I would suggest you have C3 for lack of rcd for additional protection on some circuits , and C3 for lack of rcd for some circuits having cables less than 50mm below the surface, and little else worth worrying about, none of which would give unsatisfactory!
 
.
Circuit 11 an untraced circuit indicates a 2.5 radial on a 32A protective device and that in itself to me is a Code 2. They have managed a Zs for it though.
I wish I possessed the magic powers to be able to measure untraceable circuits.
I despair at peoples lack of ability to produce plausible fake results…
 
Circuit 11 an untraced circuit indicates a 2.5 radial on a 32A protective device and that in itself to me is a Code 2. They have managed a Zs for it though.
Other than the nonsense of an incorrect Zs, without knowing what is on the end, there may not be a problem.

If it is a fixed load, or a single fused outlet/FCU then overload protection is not required, so we can't know for sure that it's incorrect
 
I'd get in touch with the person who did that report, say you've taken advice, and
1) you can't have an unsatisfactory report with only C3's
2) the two C3's don't stack up anyway, RCD protection is not needed for fault protection as disconnection times are met on all circuits, and RCD protection is not needed for fire protection as it isn't a farm.
If they don't apologise for their mistake and issue a satisfactory one, then plan B would be to get a letter saying all (fabricated) remedial work has been carried out and the installation is now satisfactory. Any competent sparks could have a look and do that for you, and this meets the PRS scheme obligations.

What's the first half of the postcode? Someone might offer to help you.
The first half of the postcode is B23.
 

Reply to Can an EICR be unsatisfactory with only C3 codes? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
605
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock