Circuit 11 an untraced circuit indicates a 2.5 radial on a 32A protective device and that in itself to me is a Code 2. They have managed a Zs for it though.
Other than the nonsense of an incorrect Zs, without knowing what is on the end, there may not be a problem.

If it is a fixed load, or a single fused outlet/FCU then overload protection is not required, so we can't know for sure that it's incorrect
 
I'd get in touch with the person who did that report, say you've taken advice, and
1) you can't have an unsatisfactory report with only C3's
2) the two C3's don't stack up anyway, RCD protection is not needed for fault protection as disconnection times are met on all circuits, and RCD protection is not needed for fire protection as it isn't a farm.
If they don't apologise for their mistake and issue a satisfactory one, then plan B would be to get a letter saying all (fabricated) remedial work has been carried out and the installation is now satisfactory. Any competent sparks could have a look and do that for you, and this meets the PRS scheme obligations.

What's the first half of the postcode? Someone might offer to help you.
The first half of the postcode is B23.
 

Reply to Can an EICR be unsatisfactory with only C3 codes? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
615
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock