Hi Guys just replaced a 200 amp main isolator in a factory along with a replacement 3 phase board should you do an installation cert or a minor works as it's like for like
 
Before we start anything like this we like to get as much information eg existing certificates, circuit charts etc and turn off each circuit to prove what it feeds so when reinstalled we know what it does for retesting and is safe to bring back into service.
 
Got the old certs for the board mainly concerned about the main isolator I'm tempted to issue a minor works for it but would any one issue different
As Westward10 (who beat me to it while I made a cup of tea) posted I would do an EIC this is more than minor works you have the circuits in the distribution board to consider. You are required to put this information on the certificate anyway.
 
You need an Electrical installation certificate for the new board and all finals circuits within, plus the new isolator.

All tests will be from an initial verification prospective and will include all tests performed in the sequence stated.

Apologies if I'm telling you how to suck eggs
 

Reply to Certificate for replacing a main 200amp isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
906
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains...
Replies
16
Views
1K
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock