I have a 17 way BG consumer unit I have set up with dual RCD. I got the 25mm tail kit, but can work out how to get 2 live tails into the bottom of the main switch to connect to the RCDs. Any ideas please?
 
Can we have a photo?

normally, the tails go into a main switch, then there are made up tails feeding each of the rcds from the load side of the switch.
These should be included in the consumer unit what purchased.
 
BG are not the greatest units in the universe, if you have the chance to return it I'd do so and get something decent.
Nothing wrong with dual-rcd boards, but the current fashion is a main switch and a RCBO for each circuit combining RCD and over-current protection for each circuit.
(The Fusebox brand is very popular as not costing the earth but is good quality. )
 
If i were you i would return it and buy the correct board of a different brand. Or I would use rcbos and abandon the dual RCD plan, bg ones are not that expensive.
 
Well, I think you can buy a conversion kit which has the right link cables at the right lengths.

your 17 way board will only be 13 when you add in a couple of rcds
I can’t seem to find a kit for dual RCD where the lives are linked. The other thing I’ve noticed is when you bend the tails to fit them it’s difficult to not have exposed copper, as the insulation pulls away. Any idea where you get shrouds from.
 
not compulsory, but the customer has to "opt out" of having it.

I think Screwfix are trying to sell off their non-spd BG boards on special offers.
Same advert said "buy this, and get 25% off 25mm tails"
Yeh... on blue and brown 6181Y... no mention of the 6491X green/yellow
 
not compulsory, but the customer has to "opt out" of having it.

I think Screwfix are trying to sell off their non-spd BG boards on special offers.
Same advert said "buy this, and get 25% off 25mm tails"
Yeh... on blue and brown 6181Y... no mention of the 6491X green/yellow
That’s fine, the ”customer“ is me. I’m a newby electrician, so I thought it best to make all the mistakes on my own house first ?
 
As asked earlier... how many neutral bars are in this bare bones box?

For 2 RCD's, you would need 2 bars... one bar protected by each rcd.

Apologies if this has been answered
 
as previous replies. go the whole hog and fit RCBOs. this will also give you more useable ways than a dual RCD board, and eliminate the need for those dreadful floppy interconnection tails.
 
it's in his own house, so he should go for top dollar gear. RCBOs all the way. notlike us oldies where own house electrics were 80% equipment salvaged from job upgrades. 16 sockets in the house, and never 2 the same. CU that complied 3 editions ago.
 
maybe OP is talking about the internal links to each RCD .
But how would a qualified electrician not know how to do that? Not bashing him, just confused.

Electrician to electrician questions are usually things like 'are my calculations right here' or 'how would you route this...' not 'how do i get power to a board'. ?
 
Don't know if I'm missing something but there seems to be a lack of job planning on the part of the OP
Surely you make sure you have all the materials and the correct materials to complete the job before starting it, as stated previously by others for me the best route would be RCBO's, to buy a CU with a main switch then populate it with a couple of RCD's doesn't sound a cost effective way to get a dual RCD CU to me
 
As I understand it, the OP is newly qualified… maybe doesn’t know how CUs are supplied, whether had to build them from scratch, buy them populated or part populated… split board etc. Lot to think about if you haven’t done them before.

At least he’s practicing in his own house.
I wonder if, and again no offence OP, he did a shorter course or something?
 
A quick search of the usual suppliers are not throwing up ready-to-roll dual RCD link leads with the two lives in one dual ferrule (as you get with a new populated board) only split load kits with 2 Neutral links and 1 Live link.

If finances permit it I'd still cut my losses and go for RCBO's though - much easier!
If you need to make what you have work, options as I see it are:
a) get virtually any 2nd hand dual RCD CU from ebay and steal the link cables. (around £20) This is probably the cheapest way out of the mess, nasty as it is.
b) get a normal split load kit (£15), a ferrule crimper and bootlace ferrules (£10-£30) chop up the live to create a short lead and a longer lead and put new bootlace ferrules on the ends, thus creating two leads with the same ferrule on one end of them. Hopefully they would fit in the main switch terminal side by side. Otherwise you can get dual bootlace ferrules to take two cables but they aren't cheap.

(I really would go for the RCBO's if at all possible!)
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

01E5945C-CCFA-4AB3-906A-F803F8862A43.jpeg

Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
 
A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6…
That is a good thing, as you might want to shuffle the loads around, but...
but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
<= this is absolute crap!

FFS we get told in the regs to only use the manufacturer-approved parts so they fit properly, etc, and then we have examples that are pretty much "meh, it goes in at a push"
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
I'm unlikely to be fitting domestic CU but this has been very informative as a reason not to go with ones of these.
 
the reason the busbars slant is if you push them too far into the MCBs. i never had any trouble with BG.
 
the reason the busbars slant is if you push them too far into the MCBs. i never had any trouble with BG.
Just me. I like to push the busbar as far up as I can, thinking the terminal gets the best grip. I suppose I could set it directly horizontal.

Also, might be the fact the CU is fitted tight in a corner, high up at the ceiling and I was tightening with the wrong hand… made everything slant.

Putting the lid on, kept hitting the RCD button
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

View attachment 90346
Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
Not a bad design overall the dual RCD board

DP main isolation

All circuits RCD protected

Overcurrent protection provided by dno

The lighting on shared rcds would be the only issue with it imo
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

View attachment 90346
Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
I was moaning about this very morning regarding the location of the 30mm knockout, you have to assume that it’s not designed by sparks ?
 

Reply to Connecting Dual RCD board. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
309
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
353
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
I've got a dual rcd mk sentry board that I want to inverter into an rcbo board. If I link the two neutral bars from the main switch is this OK to...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock