  1. Simon Linton
    Offline

    Simon Linton EF Member

    Location:
    Altrincham, Cheshire
    Business Name:
    Simon Linton - Domestic Electrician
    I am about to start a job where the existing wiring from a detached garage is 2x6mm SWA. This runs underground from the garage consumer unit to the house and is connected, via a Junction box, to a ring circuit in the basement.
    I plan put the supply to the garage onto it's own circuit (32A) using 6mm Twin and Earth cale from consumer unit in the house and connecting this, inside the house, to the existing SWA cable. Do any members know if there is a junction box that will connect SWA cable (using a gland) to Twin and Earth?
     
  2. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Use a standard steel adaptable box, Armoured gland into one side & standard Sprint or similar cable gland into the other for the 6mm. Use Wago's to make the splice, Screw solidly to a wall or beam, wall preferably.
     
    • Agree Agree x 2
    Last edited: Jun 22, 2017
  3. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    It's not been previously connected by an electronics graduate has it ?
     
    • Funny Funny x 13
    • Like Like x 1
    • Winner Winner x 1
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    why 2 x 6mm SWA? do you mean 2 cables or a 2 core SWA?

    what's the earthing system, and are ther extraneous metal parts in the garage?
     
    • Like Like x 2
  5. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    I am holding my breath on this one!
     
    • Funny Funny x 1
  6. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    you need to change your picture aviator page simon linton was it took in prison !
     
    • Agree Agree x 1
    • Friendly Friendly x 1
  7. Simon Linton
    Offline

    Simon Linton EF Member

    Location:
    Altrincham, Cheshire
    Business Name:
    Simon Linton - Domestic Electrician
    Thanks for the prompt advice. I have located all the items at Screwfix. Although I love Wago they only go up to 4mm so I'll have to use a 6mm terminal blocks. for the connection. Thanks again.
     
    • Agree Agree x 1
    • Disagree Disagree x 1
  8. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    ones you get them a then your hooked!
     
    • Bad Spelling Bad Spelling x 1
  9. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    • Agree Agree x 2
    • Informative Informative x 1
  10. Simon Linton
    Offline

    Simon Linton EF Member

    Location:
    Altrincham, Cheshire
    Business Name:
    Simon Linton - Domestic Electrician
    I didn't think anyone would know if I cropped my number off!. How perceptive of you to notice. I assume you have also done t
    Thanks for making me aware of this. I use the 221 connectors but these 773-173 will be great. A bit expensive at £17 for 50 from my supplier (34p each!)
     
  11. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Try going to TLC they sell them in singles.
     
  12. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
  13. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    not paying my taxes on time robbing banks,& stealing lolly pops from kid mouths !
     
    • Funny Funny x 2
  14. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    No Simon, if you look at a decent Electrical wholesaler you'll find they go to 6mm.
    I keep some in my service kit.
     
  15. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    what is the services to the property TN-C-S or TT or TN-S
     
  16. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Why do you want to extend SWA with T&E?
    I was taught that you should always extend a wiring system with either the same type or another type which has equal or better protection.
     
    • Agree Agree x 3
  17. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Presumably because the new section of cable will be inside the house where SWA won't be required (depending on installation method).
     
    • Agree Agree x 2
  18. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Have we not done this thread before??
     
    • Agree Agree x 2
  19. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    ^^ multiple times:)
     
  20. Spoon
    Offline

    Spoon Trusted Advisor

    Location:
    Lancashire
    It's like chocolate... or Lion's Midget Gems.... You can never have enough...
     
    • Like Like x 1
    • Funny Funny x 1
  21. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Makes you sick after a while though ;)
     
    • Like Like x 1
  22. Spoon
    Offline

    Spoon Trusted Advisor

    Location:
    Lancashire
    You wuss..... :tearsofjoy::tearsofjoy:
     
  23. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    It's like real ale... or Laphroaig.... You can never have enough...

    corrected that for you. ;)
     
    • Like Like x 1
    • Agree Agree x 1
  24. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Never liked chocolate anyway, always preferred savoury.
     
  25. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    or willy w**kers bar
     
  26. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    hate milk chocolate. makes me puke. now real dark chocolate, cut into chips, mixed with cornish ice cream, 2 fl.oz. of JD drizzled over,strawberry sauce on top, now that's living.
     
  27. Spoon
    Offline

    Spoon Trusted Advisor

    Location:
    Lancashire
    I hope it's not just my posts that send threads flying off at a tangent.... :tearsofjoy::tearsofjoy:
     
    • Funny Funny x 1
  28. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Now good quality dark chocolate is not bad at all, my middle daughter loves the stuff. She'd pick that over any chocolate.
     
  29. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    well, if you put some crap on a spoon and flick it, that's a tangent.
     
    • Agree Agree x 1
    • Funny Funny x 1
  30. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    remember Bourneville, dark chocolate good old British bar.
    now made by kr*p kraft yank doodle company. and now the bars are getting smaller.
     
    • Agree Agree x 1
  31. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    That is disgusting. My estimation of you has gone right down.
    How could you steal a child's lollypop.
     
    • Funny Funny x 1
  32. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    easy hood wink them ,rip it out of their mouths and shove a dummy in
    kids love strawberry lolly pops!
     
    • Funny Funny x 1
  33. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    Take it you do too lol. :)
     
    • Like Like x 1
  34. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    have you see a kid with ice cream around the mouth,and watch the pet dog next to
    him, boy the dog loves ice cream which one will eat the cornet first !
     
  35. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    That made me smile , I have seen that . My dog used to drool watching my kids eating ice cream; that was after she had devoured her own .
    Golden memories.
     
    • Like Like x 1
  36. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    @Simon Linton@Simon Linton How do you plan to provide the earth?
    First of all, physically at the box you have chosen.
    Secondly, I guess you are using the SWA? will the steel armour meet the requirements? Or are you TT'ing the distant end?
     
    • Agree Agree x 1
  37. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Fair enough, but wouldn't you use a cable which allows you to keep the cpc the same size for the whole run?
     
    • Agree Agree x 1
  38. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    I'd certainly have a little think about whether it mattered or not. In many cases it won't, provided that the cpc meets the minimum requirements over the whole length of the circuit. If the T&E runs into the board, it'll be obvious that the circuit has more than one cable type. If someone was to insert a piece of T&E into the middle of a run of SWA, I'd be less likely to approve.
     
    • Agree Agree x 1
  39. SWD
    Offline

    SWD Gender neutral Electrician's Arms

    Location:
    London
    Has the OP's question been answered or has the chocolate vs savoury battle been won ;o))))))
     
    • Like Like x 1
  40. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    The OP's question has been answered, Chocolate / Savoury battle: Jury still out :D
     
    • Funny Funny x 1
  41. Simon Linton
    Offline

    Simon Linton EF Member

    Location:
    Altrincham, Cheshire
    Business Name:
    Simon Linton - Domestic Electrician
    I mean 2 core SWA.
    Earthing system is TN-S
    There are no extraneous metal parts in the garage, which is brick built.
     
    • Like Like x 1
  42. Simon Linton
    Offline

    Simon Linton EF Member

    Location:
    Altrincham, Cheshire
    Business Name:
    Simon Linton - Domestic Electrician
    The SWA goes to the basement inside the house so the 6mm twin and earth will be all be indoors and clipped back to the house consumer unit.
     