I am about to start a job where the existing wiring from a detached garage is 2x6mm SWA. This runs underground from the garage consumer unit to the house and is connected, via a Junction box, to a ring circuit in the basement.
I plan put the supply to the garage onto it's own circuit (32A) using 6mm Twin and Earth cale from consumer unit in the house and connecting this, inside the house, to the existing SWA cable. Do any members know if there is a junction box that will connect SWA cable (using a gland) to Twin and Earth?
 
Use a standard steel adaptable box, Armoured gland into one side & standard Sprint or similar cable gland into the other for the 6mm. Use Wago's to make the splice, Screw solidly to a wall or beam, wall preferably.
 
Last edited by a moderator:
I am about to start a job where the existing wiring from a detached garage is 2x6mm SWA. This runs underground from the garage consumer unit to the house and is connected, via a Junction box, to a ring circuit in the basement.
I plan put the supply to the garage onto it's own circuit (32A) using 6mm Twin and Earth cale from consumer unit in the house and connecting this, inside the house, to the existing SWA cable. Do any members know if there is a junction box that will connect SWA cable (using a gland) to Twin and Earth?
why 2 x 6mm SWA? do you mean 2 cables or a 2 core SWA?

what's the earthing system, and are ther extraneous metal parts in the garage?
 
Use a standard steel adaptable box, Armoured gland into one side & standard Sprint or similar cable gland into the other for the 6mm. Use Wago's to make the splice, Screw solidly to a wall or beam, wall preferably.
Thanks for the prompt advice. I have located all the items at Screwfix. Although I love Wago they only go up to 4mm so I'll have to use a 6mm terminal blocks. for the connection. Thanks again.
 
you need to change your picture aviator page simon linton was it took in prison !
I didn't think anyone would know if I cropped my number off!. How perceptive of you to notice. I assume you have also done t
Thanks for making me aware of this. I use the 221 connectors but these 773-173 will be great. A bit expensive at £17 for 50 from my supplier (34p each!)
 
Thanks for the prompt advice. I have located all the items at Screwfix. Although I love Wago they only go up to 4mm so I'll have to use a 6mm terminal blocks. for the connection. Thanks again.

No Simon, if you look at a decent Electrical wholesaler you'll find they go to 6mm.
I keep some in my service kit.
 

Reply to Connecting SWA to Twin and Earth cable? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
193
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
491

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock