Hi , quick question , in my thoughts requires a quick answer
160amp fused switch feeding existing Hagar panel board fine no problem with that
My superior wants to install a new 125amp rated DB fed from same switch ?
I don't I would want to see a board rated at 160amp or above
Thoughts please
 
Hi , quick question , in my thoughts requires a quick answer
160amp fused switch feeding existing Hagar panel board fine no problem with that
My superior wants to install a new 125amp rated DB fed from same switch ?
I don't I would want to see a board rated at 160amp or above
Thoughts please

Why?? Just change the fuses out to 125A.
The size of the fuse switch is basically just a frame size, same as a DNO's service cut out, where the max fuse rating is say a 100A, but can accomodate anything from say 20A to 100A
 
think OP means a 2nd 160A DB parallelled with an existing 160A DB, both on a 160A fuse
 
Correct . Can't change the fuse . The rating as far as I gather is the bus bars in the board . Surely they must be rated to the protective device ?
 
The 160amp fuse is there to protect the submain cable, any switchgear attached should be rated to the upstream fusing i.e. 160A in this case unless due to design parameters where the board cannot pull more than the main switch can handle due to say the sum of the protective devices downstream limits possible FLC (Although its good practice to match the switchgear even in this case to allow for expansion and alteration).

2 x 160amp off one is fine if demand has been worked out to satisfy this set up, although I would have the 160amp front end feed a small busbar chamber and 2 individual Isolators for the DB's
 
Last edited:
Correct . Can't change the fuse . The rating as far as I gather is the bus bars in the board . Surely they must be rated to the protective device ?


Why can't you change the fuse(s)??

Would you design an installation where the total current expected of the individual circuits of a DB is going to be in excess of the rating of the DB, i HOPE NOT!!
 
Why can't you change the fuse(s)??

Would you design an installation where the total current expected of the individual circuits of a DB is going to be in excess of the rating of the DB, i HOPE NOT!!
Eng I havnt designed anything this is an existing supermarket with existing distribution connected and yes your right about the design aspect . However someone far more worthy than me has done this previous . This scenario is an add on which I am arguing with my gaffer about . In essence I see the bussbar as just a link of copper so therefore the fused switch device is there to protect the sub feed and the links through the DB . I appreciate that some maths wizard will whistle of some equation about withstand and PSCC and all that which would be fine . But trust me my boss would look at it and throw it in the bin cos he wouldn't understand it . The design with regards to bussbar chamber I had thought of . Costs prevail unfortunately . Thanks guys
 
The 160amp fuse is there to protect the submain cable, any switchgear attached should be rated to the upstream fusing i.e. 160A in this case unless due to design parameters where the board cannot pull more than the main switch can handle due to say the sum of the protective devices downstream limits possible FLC (Although its good practice to match the switchgear even in this case to allow for expansion and alteration).

2 x 160amp off one is fine if demand has been worked out to satisfy this set up, although I would have the 160amp front end feed a small busbar chamber and 2 individual Isolators for the DB's

Providing the 160A switch fuse supply is sufficient to supply both of these DB's then like you the inclusion of a busbar chamber and isolators/switch fuses for the DB's is the way i'd go too. However i can't see why you'd need both DB's to be rated to the 160A switch fuse....
 
Thanks Eng . Like you the buss chamber with the two isolators is the way forward . Another option maybe would be to have another sub feed from the existing switch feeding an 125amp switch fuse then into an 125amp rated DB ? . I understand the outgoing would in theory limit the draw but knowing how they work someone else will probably come along and drop another say 63amp breaker in there for some humongous bit of kit and I would worry the board would not be sufficiently rated and guess what it's my arse that's on the dotted line . Cheers
 

Reply to Distribution Board Rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
776
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock