When conducting an EICR you are inspecting and testing the fixed wiring, power consuming items, such as hand driers etc are NOT part of the fixed wiring, to put it in perspective would you ISITEE (PATest) during an EICR? answer not unless you have charged the client for testing these items, it's a separate job to be priced separately. Unless these tests are in the price for the EICR I can visualise the EICR being very time consuming, more than you would normally expect. The need to document all these items would add hours to an EICR.No, however I'm interested to what members do on here as I've always taken the view that portable appliances with a plug was tested with a PAT tester and fixed appliances was part of the electrical installation and done on the EICR.
Refer to part 5 of the CoP for types of equipment, the equipment does not need to be plugged in to be tested, I would suggest to those in doubt read the CoP and inwardly digest.The problem is caused almost entirely by the term 'PAT testing'. a) much of it is inspection rather than test, and b) it's not just plug-in portable equipment that needs to be tested (fridges aren't portable for instance, but need inspection/test).
As Pete says above, the correct term is ISITEE, and is governed by the code of practice. All is explained in there (well mostly all - it does leave a few things open).
Some hotels put hairdriers, trouser presses etc. on FCUs, but they are not part of the fixed wiring as such, and they need testing (or inspecting, as appropriate).
The deciding factor is not whether the item has a plug on or not.
I wish the term 'PAT test' had never been invented - I spend much time explaining things to people because of this!
The ISITEE is not a statutory document but those listed in #8 are and how you comply may lead you to this CoP.