• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Double insulated down lights cpc in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
0
whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

Double insulated down lights cpc 94E4DDFB-0368-4B1E-98C0-81BC1A837D67 - EletriciansForums.net
 
whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

View attachment 44575
that's disgraceful.the Wago logo should be facing the camera. :D:D:D.
 
it's difficult,personally snip it off.
Can't really see a problem,it's connected at other end.
May seem a bit rough,but manufacture should have an earth terminal .
 
it's difficult,personally snip it off.
Can't really see a problem,it's connected at other end.
May seem a bit rough,but manufacture should have an earth terminal .
If it’s one of many, the CPC needs to continue to the next fitting.
Snipping off would not be an option.
Easiest solution, is to trim back the cable sheath so the CPC can be connected outside of the enclosure.
 
Could have found some bigger green/yellow sleeving :D.
Red crimp would fit down the side of the terminal block?
 
If it’s one of many, the CPC needs to continue to the next fitting.
Snipping off would not be an option.
Easiest solution, is to trim back the cable sheath so the CPC can be connected outside of the enclosure.
Like people did at the old circular junction boxes, just leave them not suitably enclosed.
 
Click Flow connectors.
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
And how would it be connected to the Earthing arrangement if there is more than one luminaire?
 
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
 