polo1

-
Arms
Reaction score
633
Testing during a board change, a RFC on a 32A 60898, with rcd protection, you find that the max Zs is exceeded by 0.1 ohms using the no trip setting on your mf tester
On the EIC do you -
A) simply record the actual measured value
B) record the actual measured value and note the position under comments on the installation
C) retest, bypassing the rcd, on the Hi setting of the tester and record the revised value
D) change the ocpd to a lower value to achieve compliance with max Zs
E) do something different?

There's a round of drinks riding on this, so think carefully!
 
It is a board change so not much you can do about the Zs so use the rcd for fault protection.
 
Don't understand why the Zs is so high with those readings, ditch the rcd and test on high.
 
The R1 & R2 must have been obtained at a spur on the RFC ? Regardless you have a Zs of 0.79 which is well under the max value for a 32a B type OCPD ?
 
The R1 & R2 must have been obtained at a spur on the RFC ? Regardless you have a Zs of 0.79 which is well under the max value for a 32a B type OCPD ?
This is what I worked out to max to bs7671 on ocpd is 1.37 O.P. said +0.1 that gives 1.47 ????????? even at 80% I make it 1.09 + 0.1 =1.19
 
Test a few more times and take the best reading. Tin hat on and suitably bonded to the nearest window frame/radiator :)
Daz
 

Reply to Exceeding max adjusted Zs on a board change. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just processing an EICR and noticed a couple of final circuits measured Zs values (fed from a sub distribution board) slightly exceed the Max...
Replies
24
Views
12K
Bobster
B
Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
D
Given that Amd3 reduced max Zs values slightly what is everyone coding if a measured reading falls between the pre Amd3 value and the post Amd3...
Replies
73
Views
10K
Deleted member 9648
D
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
E
Hi, quick question....long answer!! An RCD has been installed in a single phase circuit as the measured Zs exceeds mcb. Circuit's wired in...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock