Discuss Fault has stumped me!! in the UK Electrical Forum area at ElectriciansForums.net

E

Eddiesparks

Did a board change today and put in rcbos for mcbs in common areas of a block of flats. Meggered out ok before i started by the way!!

Rcbo for outside lights didnt hold. Mcb was fine before. All others held fine. So neutral to earth fault right? Also disconnected neutral from rcbo no problems til neutral connected, with live connected all good. Connected neutral trip. Connected just neutral - trip. Earth in all the time.

Disconnected that circuit's earth and functional earth to see if it would hold. No joy. Traced earth and it goes nowhere, cut off at contactor! However outside lights gave me a Zs so earth must be taken off another circuit.

Thought about borrowed neutrals - but all other rcbo's held - didnt trip in a pair. Also meggered between neutrals came out ok. Even disconnected all other neutrals except outside lights. No joy.

It's a main board in common areas that feeds that building's power and lights and outside lights plus feeds a few submains. Flats are on separate main incomer individual fuses. Could it be a borrowed neutral from a lighting circuit in one of the flats.

Also, old board had charring round where the main neutral from 100a switch meets neutral bar. Is this probably unrelated and due to bad connection??

What a horrible day. Going back tomorrow to fault find some more. But it's hard to find the ordering of the outside lights there are groups of them all over the place. I suppose get Zs on all of them and lowest is closest to the board.

Wish me luck, but more importantly some highly experienced insight would be great!!
 
Also have you IR tested the neutral of the tripping circuit to all the other neutrals whilst they're disconnected?
 
Maybe but one might win the race and prevent the other one from tripping and probably both would trip only if both circuits had load on them. If one of the circuits has zero load current then maybe it wouldn't trip. I'm not very familiar with RCBO's, we only occasionally come across them where I am so hopefully someone will confirm this or give you better info.
 
Get the offending circuit going again on an mcb. You know its not a live to earth fault otherwise the mcb would have gone. Then try and use an educated guess as to which is the first fitting in the circuit. disconnect the rest from there and get the rcbo back in. See if it holds with just the one fitting and then re connect downstream until by process of elimination you find which run of cable or fitting is giving you problems. Not very technical granted, but you will be home in time for tea.

One other point if its a borrowed neutral once the outside lights are on an mcb the borrowed circuits rcbo will start to tripp. At least you will feel like your getting somewhere
 
Get the offending circuit going again on an mcb. You know its not a live to earth fault otherwise the mcb would have gone. Then try and use an educated guess as to which is the first fitting in the circuit. disconnect the rest from there and get the rcbo back in. See if it holds with just the one fitting and then re connect downstream until by process of elimination you find which run of cable or fitting is giving you problems. Not very technical granted, but you will be home in time for tea.

One other point if its a borrowed neutral once the outside lights are on an mcb the borrowed circuits rcbo will start to tripp. At least you will feel like your getting somewhere

Put outsides on mcb til tomorrow. All other rcbos held. Thanks for advice. This confirms my suspicions not borrowed neutral. Will 'insulation resistance test' bit by bit (technical term ;-) )
 
Put outsides on mcb til tomorrow. All other rcbos held. Thanks for advice. This confirms my suspicions not borrowed neutral. Will 'insulation resistance test' bit by bit (technical term ;-) )

IR's might throw you. You have a lot of resistive loads in parallel plus feedbacks from parallel earths ect. Have you got any galv conduits in use, or gear trays going down by way of fixing screws into masonry that is damp (especially with recent weather)
Use your test gear by all means but proof of the pudding is in the eating, and trying to find an IR fault thats only a fault when RCBO is connected can be time consuming and unless your really seeing methodically what your readings mean real world scenario, things will soon get frustrating.
Process of elimination rules. Good luck, and happy hunting.
 
Thomas 1981. Tried 2 different rcbos!

Bladsparkies- yes galv conduit in use. Are u saying parallel earth could be a problem from these?? You're damn right it's frustrating!!
 
Thomas 1981. Tried 2 different rcbos!

Are u saying parallel earth could be a problem from these??!

that makes no sense , all earthing is "parallel" as it originates at the same point.

if its outside lights tripping then look for water damage in a fitting or a faulty pir / photocell , i dont see it being a borrowed neutral at all.
 
Thomas 1981. Tried 2 different rcbos!

Bladsparkies- yes galv conduit in use. Are u saying parallel earth could be a problem from these?? You're damn right it's frustrating!!

Yes galv is conductive you have another earth return, and plenty of places on route where the cables IR might be failing or a fitting gear tray. To get an accurate insulation resistance reading you will have to disconnect so much stuff. Your far better isolating parts of the circuit and trying the rcbo to see when the fault clears. That way you can narrow your search down to maybe a chaffed neutral touching the conduit or a faulty gear tray or loss of IP rating letting moisture in. Could even be a high resistance live to earth fault. Not degraded enough to throw the mcb but enough to take out a 30ma rcbo.
Like I said real world, Proof of the pudding, vs all kinds of readings that your trying to rationalise your choice. I have my preference. Go find your gremlin.

And Biff is right, its not the parallel earth path provided by the galv conduit that will cause you problems with the RCBO. BUT the galv will provide the cable with possible earth contact points on route ie chaffed cables. And that kind of scenario makes IR readings interesting.
 
Last edited by a moderator:
Boydy. Contactor is controlled by external PIR. Disconnected that and still fault. I'm there now. Lots of food for thought lads. Thank you. I'll get cracking! Ps def not L-E high resistance fault because fine with live connected. Introducing the neutral brings all the problems. I am doing what baldsparkies said and disconnecting neutrals bit by bit. I have a suspicion where roughly fault may be...
 
Boydy. Contactor is controlled by external PIR. Disconnected that and still fault. I'm there now. Lots of food for thought lads. Thank you. I'll get cracking! Ps def not L-E high resistance fault because fine with live connected. Introducing the neutral brings all the problems. I am doing what baldsparkies said and disconnecting neutrals bit by bit. I have a suspicion where roughly fault may be...

Good luck eddie let us know how you get on im intrigued!!
 

Reply to Fault has stumped me!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
447
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock