Hello,

So as a newly qualified domestic installer, I have been given a job that means getting rid of a domestic central heating system and replacing with electric heaters. Noe first thing Im going to do is upgrade the fuse board, here is the rad sizes by kw

Downstairs
1 x 2.5 kw
1 x 1.75 kw
1 x 1.0 kw
Upstairs
2 x 1.0 kw
3 x 0.5 kw

Basically, Im asking for anyones advice how they would go about running this in. Do i need to run 1 x 4mm radial to upstairs rads and 1 x 4mm for downstairs???
 
Seems like an expensive to run method of heating a property.

Personally, I would be splitting them up over more than just 2 circuits to allow some to remain in use should the OCPD or RCD operate for any reason.
 
Radial to each heater imo opinion. That way, when they realise how expensive it is to heat it that way, it will be all in place to convert to eco 7.
Does your new install comply with "an efficient way of providing heating"?
 
Problem is they got an oil boiler heating system but dont want it anymore. they wana have eco electric heaters which is beyond me. My guess is they cant afford the oil.
 
If they've been fooled into those "eco" electric heaters tell them to steer well clear. Was an article in the paper the other day about a council who had installed a load of them a couple of years ago and are how having to rip them out and install central heating.
 
8.75kw of electric heaters, they had better get an LCD meter installed or a new bearing in the old meter. Why would they not use storage heaters?
 

Reply to Fitting electric heater NOT storage. in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
213
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Got a customer with a little dilemma. They have a rental cottage attached to their main house, and have successfully let it out for a few years...
Replies
17
Views
3K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
562

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock