Discuss Garage consumer unit query in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
4
Hello, I'd like some help with my set up. I've not long moved into a house and want to have a small CU in the garage running a few sockets and a light circuit, pretty standard stuff.
At present there is a 10mm AC running from the house CU to the garage, about 30ft run, that had a metal double socket on the end of it just lying on the garage floor. The AC (live) is wired into a MCB in the house CU that also runs a few socket's!. The garage socket can be used with no issues at present.
My reason for doing this is if something happens in the garage it doesn't trip the house out.
So my question is how is best to wire it without causing tripping issues with 2 CU's ??

Cheers Dave
 
to achieve thsi you need either a hi-integrity CU with a a non-RCD protected spare way. this can be RCBO if the sub-main cable requires. or, split the tails into the CU and go from therer. not a DIY job. as mad murdoch says, call in a local electrician.
 
What Te
to achieve thsi you need either a hi-integrity CU with a a non-RCD protected spare way. this can be RCBO if the sub-main cable requires. or, split the tails into the CU and go from therer. not a DIY job. as mad murdoch says, call in a local electrician.
What Tel and Mad Murdoch said
 
Whilst this is above the class of DIY and you seem to have advocated getting an electrician in maybe post a picture of your existing consumer unit as we could be able to let you know if possible to put on an unprotected RCD way. Are you sure it is 10mm as a bit of a squeeze
to get it in a double socket?
 
It's probably 10mm in diameter of entire cable rather the CSA on a single conductor
 
IMG_20180630_143815517_HDR.jpg Apologies for the late reply, been camping for a couple of weeks in Devon with my daughter's.......as you can see the board has 2 spare ways. The armour cable core wires are the brown ( connected to a house socket MCB!) and the grey you can see connected with the rest of the neutrals. ....so how can I get my garage CU to work without tripping. It's got 2 ways on it a radial light circuit with 5 bayonets & a ring with 4 socket's, I've checked and rechecked the connections, no obvious fault .....any more advice be greatly appreciated, thanks, Dave
 
that boards looks well overcrowded. time for an upgrade to either a hi-integrity dual RCD board, or RCBOs and 1 or 2 non-RCD ways. think a 15 or 16 way would be about right. ( thats usable ways, excluding main switch and RCDs).
 
Thanks for the photos, interesting to see the swa isn't earthed by the looks on the armour.
You would need that and also some kind of protection to disconnect the swa in case of a fault. Eg separate RCD
 

Reply to Garage consumer unit query in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
812
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
481
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
736
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
755

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock