Not sure where else to go (so please don't get mad), our family electrician has run out of ideas so turning to forums for any help.

Had a new central heating cylinder fitted which allowed me to have a new mains shower fitted (replaced an old electric shower).

Every time i touch the wall (provided its wet), or the body of the shower its self, i get a 'mild' electric shock. (See video, 57V)

So i immediately called the plumber (as it didn't do this before he replaced the shower) he had no clue... so the electrician came round and earthed everything he could find (see pictures below). Removed the old electrical shower power, and did a full sweep to ultimately become stuck.

What do i do? No one seems to know the answer and I'm stuck here getting shocked every morning i shower...

[video=youtube_share;cGQgyhz9RWw]https://youtu.be/cGQgyhz9RWw[/video]

[video=youtube_share;cJSLpt63_mg]https://youtu.be/cJSLpt63_mg[/video]

[video=youtube_share;ANIRS0HTjio]https://youtu.be/ANIRS0HTjio[/video]

[video=youtube_share;uuhMQOjtIkc]https://youtu.be/uuhMQOjtIkc[/video]
 
What amazes me is the "Family electrician " has walked away left a dangerous situation.
Did he not advise to stop using the shower or recommend he disconnected the circuit causing the problem until it was sorted?

Earthing everything won't fix it if it's a live cable end buried in the wall or with a screw though it.
 
What amazes me is the "Family electrician " has walked away left a dangerous situation.
Did he not advise to stop using the shower or recommend he disconnected the circuit causing the problem until it was sorted?

Earthing everything won't fix it if it's a live cable end buried in the wall or with a screw though it.

I just checked with a multimeter, its outputting 0.007mA, which whilst isn't alarming, he did say its all linked back to the RCD's at the fuse box, so no risk to life. (I'm told)

He thought the plumber could have wired the pump up incorrectly (e.g. live and neutral mixed I'm guessing).

How can i test everything with the mains off? what am i specifically testing?
 
I just checked with a multimeter, its outputting 0.007mA, which whilst isn't alarming, he did say its all linked back to the RCD's at the fuse box, so no risk to life. (I'm told)

He thought the plumber could have wired the pump up incorrectly (e.g. live and neutral mixed I'm guessing).

How can i test everything with the mains off? what am i specifically testing?

You need a competent spark with proper test kit!
 
So my next question - can anyone recommend an electrician in Derby :smilielol5:

Part of me thought it could be the drain, but thats all plastic, or does that not matter?

For a laymen like me, i assumed earthing all the pipes would 'fix' the problem? Yet the pipes are clearly earthed yet i still get a shock. (i know earthing doesn't solve the problem, it just hides the effect it causes)
 
I understand completely, i won't use it till its fixed.

Im more trying to speed that process up by posting on here though

sorry if I'm coming off abrupt, typing on an iPhone isn't a strong point
 
Whilst bonding generally reduces the likelihood of getting shocks there are certain cases where bonding can cause a touch voltage to occur that wouldn't be present without bonding.

Given the hazardous location ie bathroom zone 1 and the fact there's a known shock hazard that's highly likely to get worse and cause injury I'd strongly recommend you firstly cordon off the shower to prevent it being used, secondly isolate the supply of the circuit causing it if possible by tripping the MCB or pulling the fuse and thirdly get an experienced electrician to come find the problem.
 
Had never thought of it like that, he's coming back round tomorrow to take another look.

Im not sure how i can isolate the circuit? There isn't any power going to the shower? its all mains fed, which is from the tank (which powers all my central heating etc).
 
locate the fused connection unit (fused spur) feeding the shower pump, switch it off and remove the fuse
 
ah. thought it was a power shower with pumped feed.
 
The pump is part of the heating system, its an unvented cylinder off the water mains.

Not sure what else i could isolate without turning the entire heating off

Safer (and easier) just not to use the shower.

Will report back tomorrow
 
If you want to try a bit of investigation yourself, turn off each circuit breaker one at a time and see if it makes any difference to the voltages you're measuring.

The fault may be nothing to do with the pump. It could be cable damage to an unrelated circuit.
 

Reply to [HELP] Electric Shock from Shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
Replies
46
Views
4K
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock