  1. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?

    37F43B79-3893-478B-A370-720DC30C907D.jpeg

    F8C5877A-6A8E-4B16-90E9-5D66621AF2BA.jpeg
     
    • Informative Informative x 1
  2. SparkyChick
    Offline

    SparkyChick Making a banana smoothy for my fave gorilla Staff Member Trusted Advisor

    Location:
    South Wales
    Business Name:
    SparkyChick
    You say Zs across L-N...

    What about the true Ze or Zdb?

    Could be someone had converted it to TNCS without DNO.

    What about a pic of the main earth terminal in the cu? And a wider shot showing all the incoming gear.
     
    • Agree Agree x 5
  3. Pete999
    Offline

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
     
    • Dislike Dislike x 1
    • Agree Agree x 1
  4. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    Sorry zdb is what I ment. Here is a full pic and there is no main earth terminal. The 6’m gas bond goes from db to the gas meter. There are a couple of dbs that there earths go back to this ‘main’ db. But this main db only has gas bond earth in it. Nothing else

    9E8783C8-8C0F-4EA0-BC95-56C037093F0D.jpeg

    D6C56C7F-77EC-4DAA-A2C1-46F0FB91B37C.jpeg
     
  5. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    It's a burry pic but I think that's a 100A DP isolator with red/black T&E passing through brown/blue shrouds of some sort.
     
    • Agree Agree x 4
    • Like Like x 1
    • Winner Winner x 1
  6. Pete999
    Offline

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Wassat blue jobby mid righhand of piccy?
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    looks like some cowboy has taken a T/E feed from that D/P switch and split the cores.
     
    • Like Like x 1
  8. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    Yes that’s right which was done by meter fitter. This could be a multitude of problems. But atm I neee to find an earth
     
  9. Pete999
    Offline

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    Yes me also, wasn't sure
     
  10. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    That’s my new db I’m installing for solar taken the neutral out to drill hole for main tails.
     
  11. Pete999
    Offline

    Pete999 Trusted Advisor

    Location:
    Northampton
    Business Name:
    None
    An earth rod outside direct to CU earthbar?
     
  12. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    Can’t see how tho as there is one 6mm earth in db which is gas bond
     
  13. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Could be a much smaller cable to the rod. Readings you are getting would not make me think rod though.

    Supp bonding from cpc to pipework that is shared with next door's pipework that is bonded and connected to their PME ?
     
    • Informative Informative x 1
  14. Steve93
    Offline

    Steve93 Trainee Access

    Location:
    Southampton
    It’s a old detached house which is a fair few meters away from neighbour. I am stumped atm
     
  15. essex
    Offline

    essex Trusted Advisor

    Location:
    Wiltshire
    It is not a DP MCB and it is not what the op asked for help on......
     