Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?
View attachment 44800
View attachment 44801
You say Zs across L-N...
What about the true Ze or Zdb?
Could be someone had converted it to TNCS without DNO.
What about a pic of the main earth terminal in the cu? And a wider shot showing all the incoming gear.
Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
Wassat blue jobby mid righhand of piccy?Sorry zdb is what I ment. Here is a full pic and there is no main earth terminal. The 6’m gas bond goes from db to the gas meter. There are a couple of dbs that there earths go back to this ‘main’ db. But this main db only has gas bond earth in it. Nothing else
View attachment 44802
View attachment 44803
looks like some cowboy has taken a T/E feed from that D/P switch and split the cores.Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
Yes that’s right which was done by meter fitter. This could be a multitude of problems. But atm I neee to find an earthIt's a burry pic but I think that's a 100A DP isolator with red/black T&E passing through brown/blue shrouds of some sort.
Yes me also, wasn't surelooks like some cowboy has taken a T/E feed from that D/P switch and split the cores.
That’s my new db I’m installing for solar taken the neutral out to drill hole for main tails.Wassat blue jobby mid righhand of piccy?