Discuss Help! Never seen this before! in the UK Electrical Forum area at ElectriciansForums.net

I think you need to disconnect earths one at a time and see how the Ze fluctuates and hopefully when you remove one the results will go up massively. This should then point you in the right direction to where the the earth is currently coming from.

I would not resort to an earth rod yet until you get to the bottom of the where the earth is coming from currently.
 
That is a lead sheathed cable coming in which should be connected to the ISCO sealing chamber and other ISCO boxes.

Inspect and test the cover of the sealing chamber to see if it is connected to the lead sheath and then test it to see if it gives a good Ze.
 
Just t
That is a lead sheathed cable coming in which should be connected to the ISCO sealing chamber and other ISCO boxes.

Inspect and test the cover of the sealing chamber to see if it is connected to the lead sheath and then test it to see if it gives a good Ze.
just tried that and it wouldn’t pick an Earth up from the casing
 
image.jpg
This is a page from the 1940 WT Henley jointing manual showing how to install these cutouts. You can see the earthing wire which should connect to the screws on the top of the cutouts and front of the sealing chamber.
 
Steve93, I agree with the others about checking the present earthing config although you might find it has been relying on the gas bond, and anything else providing a bit of continuity is purely by luck. The service cable almost certainly has a good earth on its sheath although it doesn't look like it was made off.

But what interests me is that ISCo service head. That was probably a 3-wire DC service originally, pos and neg lines with separate cutouts (in this case each with two fuses) and a neutral. These are very scarce now and if the DNO are called to replace it, I will happily send you some loot to give them a drink to leave it behind, and ship it to us for the museum. Please give me a shout if you go down that route!
 
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.
 
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.
DNO coming on a slow boat from China? that lead time is a disgrace.
 
I’ve explained. There are final circuits and one 6mm which goes to the gas bond only! Nothing else no main earth nothing. Just the earths from the circuits
 
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.

Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
 

Reply to Help! Never seen this before! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
473
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
732
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock