Discuss How big must the earth conductor be ??? in the Canada area at ElectriciansForums.net

C

chocolate

Problem !!! Hope someone knows where to find this out.

Got a SWA 4-core ( assume that the conductor size is in excess of 100mm2 ). It connects to a metal bus-bar chamber. The armour is acting as the CPC.

The chamber has no earth bar but has a earthing bolt, and relies on the casing to act as the protective conductor from the chamber to associated fused isolators all mounted on a steel framework.

What SIZE earthing conductor should be installed linking the gland of the incoming SWA to the earthing bolt within the chamber ???????

Should a earthing conductor also be installed between busbar chamber and each of the fused isolators - how can I verify that the chmaber and steel framework has a cross-sectional area that is acceptable for the incoming cable size and the fuse rating ?

Does any know where to find out such information ???? :confused:
 
Problem !!! Hope someone knows where to find this out.

Got a SWA 4-core ( assume that the conductor size is in excess of 100mm2 ). It connects to a metal bus-bar chamber. The armour is acting as the CPC.

The chamber has no earth bar but has a earthing bolt, and relies on the casing to act as the protective conductor from the chamber to associated fused isolators all mounted on a steel framework.

What SIZE earthing conductor should be installed linking the gland of the incoming SWA to the earthing bolt within the chamber ???????

Should a earthing conductor also be installed between busbar chamber and each of the fused isolators - how can I verify that the chmaber and steel framework has a cross-sectional area that is acceptable for the incoming cable size and the fuse rating ?

Does any know where to find out such information ???? :confused:

IMO I would install a conductor at least half the size of the line conductors
 
Install a seperate earth bar adjacent to the chamber.

From there a protective conductor at least half the size of the live conductors to the gland of the SWA, one to the earthing terminal of the chamber (belt and braces), a supp bond of the steel framework and protective conductors to each of the switchfuses.
 
As the Main live conductor is over 16mm the SWA isnt big enought o be a CPC so a seperate CPC has to be installed . I will get back to you with the chart its in the new GN1 as well as 16th

Old 16th GN1 Table D10A p154 and Table D10A P155

you have to work out the conductor size but a 100mm i would recon 50mm is ok but prov it with adiobatic.
 
As the Main live conductor is over 16mm the SWA isnt big enought o be a CPC so a seperate CPC has to be installed . I will get back to you with the chart its in the new GN1 as well as 16th

Old 16th GN1 Table D10A p154 and Table D10A P155

you have to work out the conductor size but a 100mm i would recon 50mm is ok but prov it with adiobatic.
If i recall i think that this applies to 2core swa single phase but 4core swa starts requiring additioal earth at a higher size but like yourself il have to dig the info out.
 
Hi

The CSA of the armourings of 4core SWA complies with BS7671 requirements for use as a CPC for cables upto 240mm.

Any size above this does not comply as the "k" value is insufficient.

That is not to say however that an additinal CPC should not be run, and I always do but if it was an existing installation that you had been asked to carry out work on, then you couldn't really put an argument forward for installaing one as technically it complies.

Just ensure that all joint/glands are tight and install the appropriate links from gland to earth bar etc.
 
not always lenny i have scanned tables fom GN1 17th please note 16mm cables ps i kniow 1 is upside down

pages 148 &149 on Gn1 17th edition
 

Attachments

  • scan0001.jpg
    92.4 KB · Views: 68
  • scan0002.jpg
    92.9 KB · Views: 35
Last edited:
Using regulation 543.1.4, page 130 17th edition

The nearest to your 100mm would be either 95mm² or 120mm²
Using www.prysmian.co.uk cable detail are

90mm² 4 core SWA, conductor resistance @ 20C is 0.193Ohms/km
Armour resistance 1.1 Ohms/km nominal area of armour 147mm²

120mm² 4 core SWA, conductor resistance @ 20C is 0.153 Ohms/km
Armour resistance 0.76 Ohms/km nominal area of armour 206mm²

Minimum cross-sectional area of cpc in relation to cross-sectional area of line conductor =
K1 x S
K2 2
Where K1 is the KI value of the line conductor table 43.1 chapter 43 page 77 of 17th edition
|Where K2 is the value of K for the protective conductor tables 54.2 to 54.6 page 129-30 of 17th edition
K1 = 115, K2 = 51, 115/51 = 2.255
S 95/ 2 = 47.5 or 120/2 = 60
For 90 mm² 2.255 x 47.5 = 107.1 mm² actual size 147 mm²
For 120 mm² 2.255 x 60 = 135 mm² actual size 206 mm²
 
One of my books say use the steal wire 0f swa shhould be the only earth to be used except 120mm and 400mm 2 core i will dig it out and tell u more if u want
 
the book is
guide to the wiring regulations
17t edition iee wiring regs
by Darrell locke
ECA

electrical rasearch association (era ) carried out a investigation into the merits or not running additional cpcs externally to armoured cables.

The report included a comparison of fault current with stand of the armour of cables to BS5467, using the k values given in chapter 54 of BS7671. It showed for all cables except 120mm squared and 400mm squared 2-core cables, the fault current-withstand of the armour was greater than the fault current required to operate a BS88 fuse within 5s. The 120mm cable was within a few per cent of passing and should be used unless it is intended to run the cable at full current carrying capacity.

Also, calculation of current sharing between the armour and external cpc show that if a small external cpc was run in parallel with the armour of a large cable there is a risk that the fault current-withstand of the external cpc will be exceeded. Because of this it is recommended that the cross-sectional area of the external cpc should not be less than quarter of the line conductors.
 
peteludman have a look in Guidance notes ! selection and erection there is a list ther which show you the worked sizes of SWA both 70 and 90 degree you will note 16mm 2 core and others dont cover it so suplimentay earths have to be installed.
 
I have just sent the niceic a email to find out what the score is with swa cpc so will let you know the outcome, they normaly take a couple of days to reply.
 
the book is
guide to the wiring regulations
17t edition iee wiring regs
by Darrell locke
ECA

electrical rasearch association (era ) carried out a investigation into the merits or not running additional cpcs externally to armoured cables.

The report included a comparison of fault current with stand of the armour of cables to BS5467, using the k values given in chapter 54 of BS7671. It showed for all cables except 120mm squared and 400mm squared 2-core cables, the fault current-withstand of the armour was greater than the fault current required to operate a BS88 fuse within 5s. The 120mm cable was within a few per cent of passing and should be used unless it is intended to run the cable at full current carrying capacity.

Also, calculation of current sharing between the armour and external cpc show that if a small external cpc was run in parallel with the armour of a large cable there is a risk that the fault current-withstand of the external cpc will be exceeded. Because of this it is recommended that the cross-sectional area of the external cpc should not be less than quarter of the line conductors.

fault current withstand yes but what about earth loop impedence?
 
Evening,
Just joined upto this forum after a search online for some info, hopefully someone can help me?
I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB.
My concern is that it appears they have not run a separate earth and are relying on the armouring as the CPC. I believeit should have a 25mm earth ran in alongside the SWA?.
My other problem is that the cable is now burried underground and had a tarmac road above it ect.
What are my options?
Thanks in advance
 

Reply to How big must the earth conductor be ??? in the Canada area at ElectriciansForums.net

Similar Threads

Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
962
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
I have been tasked with seeing if a site is capable of accommodating a large new installation. I have done some working out but I'm not sure if...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock