Discuss How to earth SWA to external EV charge point in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Reaction score
20
I am looking at section 722 of 18th edition for EV charge points. Section 722.411.4 imposes restrictions on the earthing arrangements for TN systems. For an external chargepoint connected to a domestic PME supply the accepted solution to avoiding the restrictions of 722.411.4.1 seems to be to provide a separate earth rod for the charge point and separate this from the PME earth i.e. an independent TT arrangement. My question is as follows: if SWA is used to feed the external chargepoint, how should the armour be earthed to avoid interconnecting the PME and the charge point's earth rod? This must be quite a common scenario for an external chargepoint fixed to a pole in a driveway.
 
Thanks Essex - I see now that corresponds to 542.1.3.3.

Where does the plastic box go? Buried under the pole and filled with gel? There isn't space in the charge point and it will look really crap to add some other box to the post. I am looking to use 4mm2 two core SWA. What cable should I use from the plastic box to the charge point?
 
Thanks Essex - I see now that corresponds to 542.1.3.3.

Where does the plastic box go? Buried under the pole and filled with gel? There isn't space in the charge point and it will look really crap to add some other box to the post. I am looking to use 4mm2 two core SWA. What cable should I use from the plastic box to the charge point?

If the charger enclosure is insulated, then gland the swa directly too it.
 
If the charger enclosure is insulated, then gland the swa directly too it.

but then you'll have 2 earthing systems within inches from each other inside the unit? might be ok as its inside the box but I dunno if I like it.....

those linked glands look good didn't know they existed
does anybody remember the "bite" glands that were like a conventional swa gland but plastic? don't think they exist anymore

could always just sleeve the armouring and fit a compression gland. obviously make off into proper gland at source end
 
but then you'll have 2 earthing systems within inches from each other inside the unit? might be ok as its inside the box but I dunno if I like it.....
could always just sleeve the armouring and fit a compression gland. obviously make off into proper gland at source end

In the meantime , this is what I, and I suspect many others would do ...

Come the 1st amendment of the 18th edition we may be adding rods to all PME sites ...............


As it stands "specialist" installers are already using PME earths from what I see ...............
 
Last edited by a moderator:
Well I have a 'normal' double external socket to fit later this week and one of its uses will be for a car charger with 13a plug connection. PME at this location and there won't be any rod going in. :D
 
From the installation guide for the POD Point solo unit EV charger:

“The POD Point Solo features an on-board monitoring system to detect low voltage supplies and potential earth problems, If such a condition is encountered the charge cycle is ended and the vehicle becomes isolated from the incoming supply and effectively becomes double insulated.
These features emit the need for the installation of an earth electrode and the POD Point Solo unit can safely be connected directly to a TN-C-S (PME) earth system without any special arrangements. The POD Point Solo complies with regulation 544.14.1 of BS7671.“
 

Reply to How to earth SWA to external EV charge point in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
Replies
10
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
465
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
I am a bit unsure of what Amendment 1 is saying regarding EV charging points and PME. I understand the existing 3 methods in section 722.411.4.1...
Replies
0
Views
962

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock