I am a new PV householder - advice please. Unbalanced strings and wrong inverter

Discuss I am a new PV householder - advice please. Unbalanced strings and wrong inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

J

juniperz

I was quoted for a Growatt-3600MTL with 16 Suntech STP 245S panels. We have a large roof, but it is hipped, so the installer proposed 12 panels on the house roof and 4 on a garage roof with same orientation and similar roof elevation. I did a bit of research on the inverter, even had a reply from Growatt saying that the panels should be connected 8 + 8.

So, today they came to install. The electrician has done all the internal wiring but they need to come back Monday to finish the panels and complete the electrical side.
2 Problems:
1) I just looked at the inverter in the attic and found it is not Growatt, but Samil SR4K4TLA1 (also badged Solar River and also known as Samil 4400w).
Any opinions on whether I am better or worse off compared with the quote? Unfortunately I am a new member so cannot post links, but I did find a test that said "A serious competitor - Samil Power's SolarRiver SR4TLA1 replaces Growatts's 5000TL as the best Asian inverter to be tested by PHOTON Lab".
(google "as the best Asian inverter to be tested by PHOTON Lab" and you will find it).

2) I don't think the panels have been wired as 8 + 8. I would like to attach a photo, but can't, but it shows 1 pairs of wires going into a hefty junction box labelled "Garage Roof DC" and another single pair of wires going into a junction box labelled "House Roof DC". Each junction box has leaving from the other end, a single pair of wires. These 4 wires go into the bottom of the inverter. Now I may know nothing about this, but that looks like 12 + 4 to me...
Am I in big trouble? If anyone wants to PM me an email address, I could send the photo if it would help, though it's pretty straight-forward.
Thanks in advance.
 
Never come across Growatt although some on here might have. Wouldn't like to say 100% but on all the inverters we have used 4 panels on a seperate tracker doesn't sound like a good idea. From memory the minimum (depending on wattage / voltage of the panels) is five. I'm assuming that they are using a twin tracker inverter hence unequal panels on the strings, or maybe that are linking them in one string although the pitch and orientaion needs to be the same to do the latter.

I would say the more concerning issue is that you have found a different inverter in the loft to that ordered. This is not good as you should get what you have paid for / been quoted for or have agreed to a variation in the contract. Generally you get a bad smell of the job when this happens. I would question this first and ask for detailed information on the configuration of string / tracker arrangement and also why you have not been consulted on this change of hardware.
 
I imagine that a 3600W inverter (as originally spec'd) is G83 compliant - capped at 16A output current.

An inverter with 4400W sounds like it may p!$$ off the DNO - and perhaps be ordered to be disconnected from the grid.

Additionally, an oversized inverter will not be as efficient. Generally speaking, an inverter should be about the same as the panel wattage for best efficiency, otherwise on dull days a big inverter can use up everything the panels produce just to remain powered-up.

So I would refuse to accept the installation.
 
There is no way you can balance 12 + 4 - even on a dual maximum power point inverter, let alone a single MMPT. A 4400w is very much over sized, I'd say send it back, but tbh your still going to face issues with a 3.6 Growatt.

The only credible design would be to use 2 inverters, even then you'd really have to split it 11+5 as you'd probably want to use a 1200SB for the smaller inverter (1.2kwp).

I suggest you halt the works immediately given the different inverter supplied, have the installer come round and prove technically that his design is correct and the system is correctly installed, tbh it sounds like your installers have not correctly designed your system and are pulling some kind of a fast one on the equipment - ask for a copy of the variation notice that the installer is required to produce under the terms of the MCS accreditation, you should have already had a copy and signed it!!
 
Hmmmm....If I was quoted for a BMW and was delivered an Audi I would at least expect an explination

Let them finish it and then ask why???

At least you have working kit and have only paid 25%
 
From a customers point of view I would say you are quite within your rights to 1. get an explanation on why you are having different kit fitted from what has been quoted. 2. You should be given detailed design information for the array. If you get 2. feel free to post it for an objective opinion. The type of thing you should ask for is a design tool report. Many invertor manufactuers have tools for designing arrays. However I would suggest playing it cool but to the point and stick to your point. If you work with your supplier but under your terms you may end up with a good system but don't be fobbed off. Hopefully you havn't had to pay a deposit so will have the upper hand. Deposits, in my view, are not required due to reduced system cost today. We always term it as balance on completion to your satisfaction and this effectively becomes as sales tool as it gives customer confidence in our work . The customer is always invited to take a look a the roof work once the hook and rail system have been fitted and also after panels are mounted. If they don't want to venture up the ladders we take photo's anyway so can show them the job - cleaning out the gutters also helps customer satisfaction as well :)
 
Although I would reject the system on the basis of the inverter, is it not possible that the installer has wired four of the roof panels with the four garage panels on one string, then the other eight roof panels on a second string?
I would ask to see the schematics of the system. The string voltages should also give an idea of how many panels per string. A four-panel string would be in the 100-150Volts range, while an eight-panel string would be in the 200-250Volts range, and a twelve-panel string would be in the 350-400Volts range.

As above posters have said: a string of four panels needs careful consideration due to limited options for inverter, although it may be that your proposed inverter can handle unbalanced strings without a major loss of efficiency.

And, as per the earlier post: I would still be concerned about an oversized inverter which might be able to exceed 16Amps output and annoy your District Network Operator, who can legally order your system to be disconnected from THEIR grid.

Whereabouts in the country are you?
 
I'm my view unbalanced string on a single tracker inverter are a non-starter. If the two arrays are put together in series then it might be ok. But if the two arrays are on different pitches of roof, again non-starter. It's not good to mix different pitches on a string. You only have to use a irradiance meter and alter the pitch to see the difference it makes. Hopefully you can use this guidance and apply it to your array and work out if it is relevant (ie on the different pitch).
 
When I contacted Growatt, their Tech Support person said:
"Max. number of parallel strings, means that you could connect 2 strings per MPP tracker. This is usefull when working with low power modules.

This particular inverter can work with the panels STP245S-20/Wd with an string between 5 and 8 panels, so 8+8 will work fine. If you 12+4 you are overloading one of the MPPT trackers (see screen shoots ).
Unless both roof are at facing the same azimuth and with the same tilt, you could physical split them 12 +4 but electrical 8+8.

Here's the 8+8 config Growatt Suntech 8+8.gif

And the 12+4Growatt Suntech 12+4.gif
 
Last edited by a moderator:
Although I would reject the system on the basis of the inverter, is it not possible that the installer has wired four of the roof panels with the four garage panels on one string, then the other eight roof panels on a second string?
I guess that is possible, but if that is the case, then his annotation on the junction boxes is misleading.
Connections.jpg
I can trace the wires actually - 1 set goes straight out through the house roof, and the other finds its way to the garage roof, so it must be 12 + 4.
 

Attachments

  • Connections.jpg
    171.2 KB · Views: 303
Oh dear, this does not look good, apart from what you have mentioned, If an inverter is mounted on a board, it has to be fire retardant, not just plywood..

It should also be correctly labeled, sorry, but a marker pen does not conform.
Post some more pics of the rest of the install, panel mounting also would be good.

We are seeing far too much of this type of work....
 
.

The inverter and isolators should be clearly labelled, including warning stickers and ideally with schematics provided nearby - here's mine (wall-mounted in a cool downstairs utility room). edit: there is also a "warning: dual supply" yellow sticker on the CU (fusebox).
The inverter is a PowerOne Aurora PVI-3600-UK (output limited to 16A to comply with DNO requirements). As per the schematic to the left of the inverter: it has a string of 7x250W and a string of 8x250W (total 3750W nominal panel output in standard test conditions)- this inverter works best with two strings of 7 or 8 panels and would not be very efficient if running with a string of four panels, while it would exceed the string limit into one MPPT of 2000W if it had more than eight panels into either input (although theoretically a single string of 16 panels could have its power split across the two trackers by connecting the two inside the inverter):

.

solar003c.jpg
 
Last edited by a moderator:
yes looks like the four panels might as well not be there as they not going to start up the MPPT! as stated above .

Tricky one they should of either used a Mastervolt 600 for the four panels then a single tracker inverter for the other 12.

or gone for solar edge the dip sticks !!!

Makes me laugh really does
 
.The inverter and isolators should be clearly labelled, including warning stickers and ideally with schematics provided nearby - here's mine (wall-mounted in a cool downstairs utility room). edit: there is also a "warning: dual supply" yellow sticker on the CU (fusebox).
Thanks FB - a couple of points. You specifically emphasise your "cool downstairs utility room". Is loft mounting a problem? It does get pretty hot there in the summer... (Standard red/brown concrete tiles).
The electrician said that he would not need to replace the consumer unit because he would be able to use one of the "ways". As yet, there is no apparent change to the CU, certainly no new labels on the 3 free ways or anything else. It is possible that this happens with the final connection - certainly the power didn't go down yesterday.
 
Thanks FB - a couple of points. You specifically emphasise your "cool downstairs utility room". Is loft mounting a problem? It does get pretty hot there in the summer... (Standard red/brown concrete tiles).
The electrician said that he would not need to replace the consumer unit because he would be able to use one of the "ways". As yet, there is no apparent change to the CU, certainly no new labels on the 3 free ways or anything else. It is possible that this happens with the final connection - certainly the power didn't go down yesterday.

Some inverters cope better than others with heat. I reckon that 40-45 degrees is possible in a loft peak summer (if we ever see a summer again in our lifetimes!).
Check the manual which comes with your inverter to see at which ambient temperature it starts to lose power. Mine is expected to lose power at ambient 40'C although its internal temperature gets to 45-50'C (according to its stored-data logs) with ambient 20-25'C without power derating - this being on sunny days when the inverter is running at or slightly above maximum power (3.75kW+ coming in from the panels and 3.6kW+ going out; yes, a system can occasionally slightly exceed its nominal performance, such as my 250W panels which, occasionally, have reached 270W output per panel in exceptionally good conditions).

The inverter which I have is not ideal for a loft (although I was offered the OUTD version if the inverter was going int the loft).

It seems as if most inverters are fitted in lofts, but I wanted mine downstairs to make it easy to see what it's doing, and easily accessible; no need to clamber around the loft. The North-facing utility room also remains much cooler and more stable temperature than the loft. Electronics prefer cool, stable-temperature locations.

If you have an inverter and isolators in the loft, you ought to also have a smoke detector in the unlikely (but theoretically possible) event of a malfunction starting a small fire which woudl spread to the junk which people inevitably hoard in the loft. There have been one or two reports of loft fires which were thought to have been started by a malfunction of the isolator switches or inverter.
 
Thanks again FB - a smoke detector sounds like good advice.

And I have an update on Roof Pitch - I have just braved the strong sunshine and rain (what IS going on?) to go on both roofs and measured the pitch:
House 30 degrees to the horizontal (12 x 245w panels)
Garage 35 degrees to the horizontal (4 x 245w panels)​
Does the collective wisdom of this forum think that this renders a single inverter of whichever brand, with one or 2 MPPTs, completely unworkable?
Does it reduce efficiency for one or both strings by a significant amount? Cause damage? Mean that 2 MPPTs is essential?

And THANK YOU. I must say I have been truly impressed by the amount of support that you have all shown to me. It is appreciated that nobody is criticising me for barely knowing what I am talking about - you are helping me learn fast.
 
You must follow advice and stop the works, it would be futile to carry on as lots of errors have already been made. Did you choose the contractor because of price or were they recommended?

You must think long term on this decision.
 
New posts

Reply to I am a new PV householder - advice please. Unbalanced strings and wrong inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock