I’d like to know if anyone else here refuses to install ring circuits in domestic premises.

For me it’s either a 20a radial / tree circuit with 2.5mm, or a 32 radial / tree circuit with 4.0mm.

Frankly I’m tired of finding broken ring circuits on 32a CB’s, as well as mismatches on end to end tests. It drives me nuts on jobs that should be simple.

I wish we would get rid of this ridiculous practice here in the UK.

I know some of you will say there’s nothing wrong with it when it’s properly installed and tested, but inevitably at some point in the future someone will come along and disconnect a conductor unknowingly while changing outlets on the circuit.

Testing is more complicated, and diagnosing faults on a ring also.
 
Nothing worse than what you call a 'tree circuit' for fault finding. Five or six legs, may be more and testing at each when installed, too. Rubbish.

I only ever make tree branches with wago boxes, with never any more than 2 cables in a socket installation box.

I always test at each socket outlet anyway so that’s no extra work.

I disagree, fault finding on a broken ring circuit with a figure 8 somewhere is worse.
 
That is utter rubbish, the rfc is the best method IMO.

Funny that.

The RFC is an artefact of materials shortage during WWII, and isn’t really used anywhere else in the world spare a few exceptions.

If it were the best method, it would have been taken up elsewhere.

I don’t know why so many electricians love the RFC other than it’s familiar
 
Funny that.

The RFC is an artefact of materials shortage during WWII, and isn’t really used anywhere else in the world spare a few exceptions.

If it were the best method, it would have been taken up elsewhere.

I don’t know why so many electricians love the RFC other than it’s familiar
During that time, after WW11, we developed the best and safest electrical supply system in the world. Even today look at some of the rubbish in foreign countries.
 
A question for the OP, what is the potential for danger, please explain as then I may make a decision as to whether it's acceptable or not?
 
Last edited by a moderator:
I think your overestimating the danger somewhat

Rfc's are great but i only really use them in kitchens now and unless its a large house would opt for 20a radials everywhere else

But lets be honest here, even in the case of a broken ring, the circuit will likely never see anywhere near enough load for any duration to be a danger of overloading the cable, unless maybe an exceptionally loaded kitchen circuit, especially given the case that even most ovens etc are on their own 16a radials now

Ive found probably hundreds of open ring circuits but next to none that i can remember with any signs of overload unless connections are loose

Id wager 90% of 32a ring circuits have never seen past 20 amps
 
Last edited:
Nothing wrong with a ring final circuit. It’s the uneducated/ unqualified who mess with them that causes the problems.

That is exactly my point. The moment you walk out of the door, someone will mess with that ring circuit in time
I think your overestimating the danger somewhat

Rfc's are great but i only really use them in kitchens now and unless its a large house would opt for 20a radials everywhere else

But lets be honest here, even in the case of a broken ring, the circuit will likely never see anywhere near enough load for any duration to be a danger of overloading the cable, unless maybe an exceptionally loaded kitchen circuit, especially given the case that even most ovens etc are on their own 16a radials now

Ive found probably hundreds of open ring circuits but next to none that i can remember with any signs of overload unless connections are loose

Id wager 90% of 32a ring circuits have never seen past 20 amps

Ok, so 10% of ring circuits do see more than 20 amps, and then what is the chance that on those ring circuits at some point a conductor will be disconnected?

This is what I find unacceptable
 
That is exactly my point. The moment you walk out of the door, someone will mess with that ring circuit in time


Ok, so 10% of ring circuits do see more than 20 amps, and then what is the chance that on those ring circuits at some point a conductor will be disconnected?

This is what I find unacceptable
that is not the fault of the design of the circuit.what is unacceptable is numpties messing with things they don't have a clue about. would you condemn gas supplies in case some idiot turned the gas on then lit a match?
 
A disconnected cpc on a RFC and the circuit will almost certainly remain safe. A disconnected cpc on a radial and everything downstream of the break will be potentially dangerous but still working. There are pro's and cons to both types of circuits, the OP has not considered the danger of a faulty radial, which can be equal to a faulty ring. Whist there are good reasons for radials, the OP's logic is not a reason to ditch rings.
 
Last edited by a moderator:
that is not the fault of the design of the circuit.what is unacceptable is numpties messing with things they don't have a clue about. would you condemn gas supplies in case some idiot turned the gas on then lit a match?

Yes but the point is people will mess with these things. With a radial or a tree, a disconnected live conductor means whatever is downstream stops working - fault is obvious and it gets checked out.

Not the case with a RFC. In my opinion that’s bad design. You have to factor this inevitability into the design, and I do, that’s why I don’t install RFC’s.
 
Funny that.

The RFC is an artefact of materials shortage during WWII, and isn’t really used anywhere else in the world spare a few exceptions.

If it were the best method, it would have been taken up elsewhere.

I don’t know why so many electricians love the RFC other than it’s familiar
I think you have to question ZEDEZ if it is likely that you are right or if a much larger number of people are right? It would be good if you could acknowledge you 'may' be wrong. I think testing a 'tree' would be a nightmare and people could add to it all over the place making it even harder. I do agree though that you do find quite a few broken rings but I still prefer them as 90% of the time they are intact and they still use less copper than a 4mm radial which can only be a good thing.
 
I instal radials all the time.
Mostly for lights.
Though one time when I added a couple of flouries to an existing circuit, I ended up making it into a ring to counter the volt drop on start up.
 
As your title suggests......'the potential for danger is too great'......

I wouldn't touch gas as I'm not qualified too......

So why do folk touch electrics whilst not qualified.......?

As I've said on another thread they deserve a belt if they get one whilst interfering!

I'm totally against what you say......rings are king!

British standards are the daddy too so we better hang on to 'our' methods......

Fcuk the rest!!
 
I prefer radials but install both rings and radials. The main reason I prefer radials is they are far quicker and easier to test, particularly if you do not know the layout as on an EICR.No other reason, certainly not the OP's reasons
 
The OP has a point here, take a ring for example after Kev the Kitchen bod has altered it, but Kev would mess a radial up as well
Kev the bod should not be touching it, the same as you should not really be messing with various other things but we all do in a way, how many times has a "professional" electrician screwed things up.
 
As your title suggests......'the potential for danger is too great'......

I wouldn't touch gas as I'm not qualified too......

So why do folk touch electrics whilst not qualified.......?

As I've said on another thread they deserve a belt if they get one whilst interfering!

I'm totally against what you say......rings are king!

British standards are the daddy too so we better hang on to 'our' methods......

Fcuk the rest!!

pfffft I have done gas work in the past and the house is still here........

haven't had a bill in 20 years though........
 
Tree circuit sounds like its going to have hidden joints somewhere to me.

Any 'electrician' who admits to installing new circuits incorporating unaccessible joints deserves an instant forum ban in my opinion!

What a complete clown.
That’s what I was thought...but was thinking no electrician would actually do this, would they? If that is the case then I’m with you and what a clown.
 

Reply to I never install ring circuits, the potential for danger is unacceptable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
Hi all. Long time lurker, first time poster. I am not an electrician but I enjoy learning as much as I can. I am currently renovating a house...
Replies
10
Views
1K
The Ghost
T
S
Greetings all, I'm looking for a bit of advice. I'm not actually an electrician, but I am an electrical design engineer and I am aware of the...
Replies
33
Views
3K
Hi guys, I have come across two problems today well acutely three so I will list them first.. 1st Testing a 4mm radial circuit today or so I...
Replies
18
Views
7K
Engineer54
E
D
Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you...
Replies
59
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock