Discuss insulation test on a ring circuit in the Australia area at ElectriciansForums.net

Q

qwertylockley

hi there, while completing an insulation test on a ring circuit i have come accross a few problems.
insulation between l-e and n-e are fine, 299megs, but insulation between l-n on both up and down rings are showing no reading, any sugestions??
r1 r2 rn are all showing low ohms on both rings, R1 + R2 are okay on both rings.
 
hi there, just found out a radio and a light plugged in, hiding behind bed!! and kitchen microwave wired in to ring behind cuboards, and not on a fused spur!!
Thanks for the help.
 
that's the reason i always put a multimeter across first.
 
I always run 250v test first but out of curiosity have you ever seen anything blown at 500v - only ever lost neons in spurs but nothing major
 
biggest problem ive seen is guys blowing up PIR's and washing machines alway test at 250 first any low reading switch the meter to continuity then test again ,oh how fun eh
 

Reply to insulation test on a ring circuit in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
618
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock