Plastic CU, no code on the next EICR as complied at the time of installation.

Cables in escape routes, no code as complied at the time of installation.

The regulations are not retrospective.


OK. And if you could not verify when it was installed because the company has gone bust? The property has changed hands many times and now no one knows if it was December 2014 or July 2015. And be honest. Who checks anyway.

But surely this is what C3s are for. Telling the user it is satisfactory but not to current standards and we recommend improvement.
 
for instance. The 16th edition you did not need to RCD protect circuits buried in a wall without earthed MP at less than 50mm. If you tested that installation today you would put that as a C3. Clearly it still obides to the 16th but things have moved on.

I wouldn't put it as a C3 personally unless someone comes up with a good reason why it should be.

RCD protection only becomes necessary when you work on/alter the circuit.
 
I wouldn't put it as a C3 personally unless someone comes up with a good reason why it should be.

RCD protection only becomes necessary when you work on/alter the circuit.

From the NICEIC:

[COLOR=rgb(32.941000%, 32.941000%, 34.510000%)]Code C3 (Improvement recommended)[/COLOR]
Observations that would usually warrant a Code C3classification include:
Absence of RCD protection for a socket-outletthat is unlikely to supply portable or mobileequipment for use outdoors, does not serve alocation containing a bath or shower, and theuse of which is otherwise not considered by theinspector to result in potential danger.
(Note: Code C2 would apply if the circuitsupplied a socket-outlet in a locationcontaining a bath or shower in accordancewith Regulation 701.512.3)


page15image14056
RCD in a consumer unit
Absence of RCD protection for cables installedat a depth of less than 50 mm from a surfaceof a wall or partition where the cables do notincorporate an earthed metallic covering, arenot enclosed in earthed metalwork, or are notmechanically protected against penetration bynails and the like
Absence of RCD protection for circuits of alocation containing a bath or shower wheresatisfactory supplementary bonding is present
 
OK. And if you could not verify when it was installed because the company has gone bust? The property has changed hands many times and now no one knows if it was December 2014 or July 2015. And be honest. Who checks anyway.

But surely this is what C3s are for. Telling the user it is satisfactory but not to current standards and we recommend improvement.

No, C3 is used to identify items which are recommended for improvement. Not for pointing out every minor non-compliance.

Would you give a C3 to an older installation which has green sleeving rather than green/yellow? Of course you wouldn't as it makes no difference to anything.

Would you give a C3 to an MET with a 'safety electrical earth' label instead of the current 'safety electrical connection' label? Again of course not, it again makes no practical difference.

You might as well give an automatic C3 to every installation containing the old wiring colours if you are going to code everything that isn't installed to current regs.
 
From the NICEIC:

[COLOR=rgb(32.941000%, 32.941000%, 34.510000%)]Code C3 (Improvement recommended)[/COLOR]
Observations that would usually warrant a Code C3classification include:
Absence of RCD protection for a socket-outletthat is unlikely to supply portable or mobileequipment for use outdoors, does not serve alocation containing a bath or shower, and theuse of which is otherwise not considered by theinspector to result in potential danger.
(Note: Code C2 would apply if the circuitsupplied a socket-outlet in a locationcontaining a bath or shower in accordancewith Regulation 701.512.3)


page15image14056
RCD in a consumer unit
Absence of RCD protection for cables installedat a depth of less than 50 mm from a surfaceof a wall or partition where the cables do notincorporate an earthed metallic covering, arenot enclosed in earthed metalwork, or are notmechanically protected against penetration bynails and the like
Absence of RCD protection for circuits of alocation containing a bath or shower wheresatisfactory supplementary bonding is present

The NIC are well known for making up their own version of the regulations !
 
From the NICEIC:

[COLOR=rgb(32.941000%, 32.941000%, 34.510000%)]Code C3 (Improvement recommended)[/COLOR]
Observations that would usually warrant a Code C3classification include:
Absence of RCD protection for a socket-outletthat is unlikely to supply portable or mobileequipment for use outdoors, does not serve alocation containing a bath or shower, and theuse of which is otherwise not considered by theinspector to result in potential danger.
(Note: Code C2 would apply if the circuitsupplied a socket-outlet in a locationcontaining a bath or shower in accordancewith Regulation 701.512.3)


page15image14056
RCD in a consumer unit
Absence of RCD protection for cables installedat a depth of less than 50 mm from a surfaceof a wall or partition where the cables do notincorporate an earthed metallic covering, arenot enclosed in earthed metalwork, or are notmechanically protected against penetration bynails and the like
Absence of RCD protection for circuits of alocation containing a bath or shower wheresatisfactory supplementary bonding is present

Neil, a word of advice, don't use the NICEIC as a reference source on here, because any credibility you've gained will go up in a puff of smoke!:smilielol5:
 
No, C3 is used to identify items which are recommended for improvement. Not for pointing out every minor non-compliance.

Would you give a C3 to an older installation which has green sleeving rather than green/yellow? Of course you wouldn't as it makes no difference to anything.

Would you give a C3 to an MET with a 'safety electrical earth' label instead of the current 'safety electrical connection' label? Again of course not, it again makes no practical difference.

You might as well give an automatic C3 to every installation containing the old wiring colours if you are going to code everything that isn't installed to current regs.


I personally would C3 those items. Not the cables colours though unless a harmonization label was not installed.
 
Neil, a word of advice, don't use the NICEIC as a reference source on here, because any credibility you've gained will go up in a puff of smoke!:smilielol5:

Thanks for the advice. My clients will not even entertain a contractor without it. I have also been taught that way. When test you test to the current regs. You woukd not test a 40 year old installation and say it is all fine because that is when it was designed. I am really struggling to understand this train of thought and I strongly disagree with it.
 
Thanks for the advice. My clients will not even entertain a contractor without it. I have also been taught that way. When test you test to the current regs. You woukd not test a 40 year old installation and say it is all fine because that is when it was designed. I am really struggling to understand this train of thought and I strongly disagree with it.
Do you do many EICR's mate?
 
It is perfectly clear, and always has been. How could you install or verify an installation to a different Standard than that to which it has been designed?

I agree, I should have made my point clearer. You would obviously verify the installation based on which ever regs it was designed to. But that's the crux of it, if I designed an installation to the now current regs and then installed it to those regs after 1st of July then verified it based on those regs, someone could come along do a periodic and decide it is non compliant with the current regs and should have been verified to the regs current to the completion date of the installation. Obviously if they had access to the original EIC and had an ounce of brain, then it would become quite clear what has occurred. I'm not in disagreement I'm just pointing out that some jobs worth could be a bit picky over it.
Personally if I find an installation to be safe after inspection, harping on about a few misnomers is ridiculous and more of a way to scam money out of poor folk.

I've had a few debates over the years with assessors from the NICEIC. One assessor even marked me down as non compliant over an insignificant misnomer. Which resulted in lots of emails and phone calls between myself and the NICEIC office. As soon as I threatened to leave the scam..scheme they soon turned it around. Hmmmm.... worried about the loss of a few bucks...!
 
Plastic CU, no code on the next EICR as complied at the time of installation.

Cables in escape routes, no code as complied at the time of installation.

The regulations are not retrospective.

They aren't retrospective, but it is completely irrelevant whether something complied at the time of installation. You can't say that something is less dangerous if it complied before but more dangerous if it didn't. The danger - perceived or otherwise - would be exactly the same.
 
"CONDITION REPORT INSPECTION SCHEDULE GUIDANCE FOR THE INSPECTOR 1. Section 1.0. Where inadequacies in the distributor’s equipment are encountered the inspector should advise the person ordering the work to inform the appropriate authority.

"2. Older installations designed prior to BS 7671:2008 may not have been provided with RCDs for additional protection. The absence of such protection should as a minimum be given a code C3 classification (item 5.12). "
 
I personally would C3 those items. Not the cables colours though unless a harmonization label was not installed.

They do not warrant a C3 code, item 1 in the below image explains all.

ImageUploadedByTapatalk1419973776.628777.jpgImageUploadedByTapatalk1419973776.628777.jpg

Having one word wrong on a label or solid green sleeving are not in any way dangerous or able to give rise to danger.

But most old installations won't have a new colours label unless they contain both wiring colours.
 
They do not warrant a C3 code, item 1 in the below image explains all.

View attachment 27379View attachment 27379

Having one word wrong on a label or solid green sleeving are not in any way dangerous or able to give rise to danger.

But most old installations won't have a new colours label unless they contain both wiring colours.


Fair comment with evidence. I will still include them in our reports but goong forward probably not code them. You cannot be wrong if you include it but you could be seen as wrong if you do not.
 
Not aware that Network Rail require contractors to be registered with the NICEIC.
The fact that I'm not registered with the NICEIC, has not prevented me from working at various sites around London.
It appears that the quote that keeps getting copied and pasted is from one of the schemes, not from the IET. As such I would not place any value on the information.
Generally, I would apply a code C3, for instances where an installation complied at the time of it's design/construction, but does not comply with the current requirements.
For instance: cables concealed in walls without an acceptable method of additional protection, socket-outlets intended for general use by ordinary persons, circuits of a location containing a bath or shower, not provided with RCD protection, time delayed RCDs set to 5s, etc.
With instances where conductors have not been correctly identified, such as switch lines, where earth sleeving has been omitted or a lable indicating two colours of wiring are present, I would just rectify, and not bother applying a code.
 
Not aware that Network Rail require contractors to be registered with the NICEIC.
The fact that I'm not registered with the NICEIC, has not prevented me from working at various sites around London.
It appears that the quote that keeps getting copied and pasted is from one of the schemes, not from the IET. As such I would not place any value on the information.
Generally, I would apply a code C3, for instances where an installation complied at the time of it's design/construction, but does not comply with the current requirements.
For instance: cables concealed in walls without an acceptable method of additional protection, socket-outlets intended for general use by ordinary persons, circuits of a location containing a bath or shower, not provided with RCD protection, time delayed RCDs set to 5s, etc.
With instances where conductors have not been correctly identified, such as switch lines, where earth sleeving has been omitted or a lable indicating two colours of wiring are present, I would just rectify, and not bother applying a code.

At risk of going off a bit. To gain RISQS (formally Link-Up) approval you will certainly require NICEIC membership. We have both.

I would also do exactly as you said above. Anything that did comply that now does not I would C3. Unless of course it was a little more serious as I am sure wevall would too. There would be no way in reality to verify when the installation was designed or installed.
 
At risk of going off a bit. To gain RISQS (formally Link-Up) approval you will certainly require NICEIC membership. We have both.
What does the RISQS initials stand for??

Sounds like someone (or Organization) has been well and truly hooked by all the hype the NICEIC spurts out!! lol!!
 
Last edited by a moderator:
They just love acronyms.
For the underground you need a LUCAS card, for Network Rail a PTS card.
Then there's the SPIC card, and a whole host of others

None of which mean anything to me. But if what UKESRail has stated is correct, then they seem to be relying on NICEIC membership to authenticate this ''RISQS'' card and maybe the others you mention here. I can't think of a worse move myself, far better to conduct your own assessment, if you're going to issue a card as a restrictive approval requirement!!
 

Reply to new reqs in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock