This would only apply if there were any services in the outbuilding which required main bonding....if a TNCS earth was used those services would have to be main bonded right back to the MET which would means a rod would be more practical.
As long as there are no services in the outbuilding requiring bonding TNCS can be used and the earth conductor sized in the normal way in relation to the line and neutral conductors.
We work closely with YEB / CE ELETRIC. on alot of UPS systems. They dont like export of a tncs earth system of anything above 25m (I think).If it has to be done they want rods in place. Might be different for other DNO's
Dont ask me why you get different answers all the time. But even the subby's crank on about it. Freedom and the like.