Disagree 200% It's about his inspection not meeting the requirements for a board change.

So you are saying that you would tell a customer they can't have a new fuseboard because the lighting circuit doesn't have a CPC

Even if he had inspected it thoroughly before he could still have gone ahead and changed the CU
 
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.
Deleted
 
Really ?????????????????????????????????
Yes I've seen it on old certs, even that made me confused. But I made inquiries, the inspector was right. However all has to be earthed. In a domestic all circuits are RCD protected but if there is a break in the R1 + R2 it defeats the objects
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.

I've seen a RCD protecting a lighting circuit (with no cpc) trip a RCD....

Do you understand how RCD's work?
 
Before, on a certificate, no CPC to lighting was classed as a c3 with advice of no metal light fittings. But in the 18th it will be a c1 or c2. Basically a fail

This is irrelevant to this thread - the OP's doing a CU change , not an EICR
 
What do you base that statement on?
Regs, looking at old certs dated 2013 and then phoning up and asking the person issuing the certs that he passed an periodic inspection even though there is no earth to lighting. I always believed with my old company that you had to earth no matter what. Apparently you could get away without CPC to lighting before, as long as there are no metal switches or fittings. That's all changing now.
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
834
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
630
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
221
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock