Discuss No power to part of the consumer unit in the DIY Electrical Advice area at ElectriciansForums.net

GKH2020

DIY
Reaction score
7
Hi,

The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer unit expecting to reset a circuit breaker but nothing had tripped.

I have attached a pic of the consumer unit. Using a current detector pen I can see that there is power feeding all of the circuits to the left of the RCD, which are the lighting circuits (lights are all working), but there is no power going to the circuits to the right of the RCD, which feed all of the sockets etc (with the exception of the hob and an oven which run from a feed where the supply enters the house, these are working). I have switched the RCD and circuit breakers on and off several times, they are definitely all in the on position but still no power.

Can anyone advise what the issue may be here please?

Many thanks in advance!
 

Attachments

  • consumer unit.jpg
    219.1 KB · Views: 33
The rcd…. Switch it fully off, then back on. Don’t use the test button to turn it off.

When that model trips, the switch goes to a mid position. It needs to be reset by turning off, then turned on.


You’ve also got wylex breakers in an MK board… you can see they don’t fit together.
 
The rcd…. Switch it fully off, then back on. Don’t use the test button to turn it off.

When that model trips, the switch goes to a mid position. It needs to be reset by turning off, then turned on.


You’ve also got wylex breakers in an MK board… you can see they don’t fit together.

Thanks for the reply. I had read about that, so have already fully switched it off and on multiple times. I am quite certain that it didn't even trip when the power went out.
 
Maybe the internal mechanism is tripping, but not the switch itself. Have you tried the test button? It should force the switch.

Over time, breakers and RCDs like this can get “welded” closed and do need regular testing to check if this has happened.


Are you certain it’s every circuit to the right of the rcd that is affected? 7-12?
If it is, then that suggests it’s the rcd or part of the internal wiring of the consumer unit that feeds the rcd.


It’s not a DIY job to replace the rcd if indeed that is what is at fault. You should employ the services of an electrician.
 
Maybe the internal mechanism is tripping, but not the switch itself. Have you tried the test button? It should force the switch.

Over time, breakers and RCDs like this can get “welded” closed and do need regular testing to check if this has happened.


Are you certain it’s every circuit to the right of the rcd that is affected? 7-12?
If it is, then that suggests it’s the rcd or part of the internal wiring of the consumer unit that feeds the rcd.


It’s not a DIY job to replace the rcd if indeed that is what is at fault. You should employ the services of an electrician.
I have tried the test switch several times and it appears to be working fine.

Definitely every circuit to the right which is affected. Interestingly, whilst I was just going through the process of switching everything off and on again in the hope of it springing back to life, I held the current detector to one of the circuits to the right as I flipped the switch up on the RCD and the circuit briefly come to life - if I apply a very small amount of inward pressure to the RCD the circuits all come to life and die again when the pressure is released. Do you think that the cause may simply be a loose connection on the RCD?

Thanks again.
 
Sounds more like the internals of the unit. Pressing against the switch will do nothing to the connections….

Again, I’ll say get an electrician involved now. I wouldn’t advise isolating the board and taking the front cover off yourself….

By the way…. “Voltage pens” are notorious for giving misleading results. Same with neon screwdrivers. Not completely useless, but don’t trust them if you’re looking for something to be dead.
 
Sounds more like the internals of the unit. Pressing against the switch will do nothing to the connections….

Again, I’ll say get an electrician involved now. I wouldn’t advise isolating the board and taking the front cover off yourself….

By the way…. “Voltage pens” are notorious for giving misleading results. Same with neon screwdrivers. Not completely useless, but don’t trust them if you’re looking for something to be dead.
I guess it doesn't really matter what the issue is - as you quite rightly point out, I'll need to get an electrician in regardless.

Thanks for your time and help.
 
I guess it doesn't really matter what the issue is - as you quite rightly point out, I'll need to get an electrician in regardless.

Thanks for your time and help.

Let us know the outcome if you don't mind.
 

Reply to No power to part of the consumer unit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
263
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
218
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
541
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
749
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock