Discuss Outbuilding on non RCD side of C/U? in the UK Electrical Forum area at ElectriciansForums.net

Because some single pole rcbo's will only disconnect the L leaving the N connected in a fault, so if you had a N - E fault the rcbo would trip, but the N - E fault would still be present and current will be flowing. the upfront s type would detect this and trip. Kind of like a backup really if that makes sense.
 
Because some single pole rcbo's will only disconnect the L leaving the N connected in a fault, so if you had a N - E fault the rcbo would trip, but the N - E fault would still be present and current will be flowing. the upfront s type would detect this and trip. Kind of like a backup really if that makes sense.

Yeah I get what you mean but don't see why you installed RCBO's. This is one time a dual RCD board would have been better. This way at least half the circuits would stay on in the event of a neutral earth fault where as in the event of a neutral earth fault with that setup your loose the lot. You may as well of installed a 30mA upfront RCD and used circuit breakers...Would of been cheaper and still would of had the same affect. If I was your assessor you would have got a bemused look from me as well :p:D
 
Yeah I get what you mean but don't see why you installed RCBO's. This is one time a dual RCD board would have been better. This way at least half the circuits would stay on in the event of a neutral earth fault where as in the event of a neutral earth fault with that setup your loose the lot. You may as well of installed a 30mA upfront RCD and used circuit breakers...Would of been cheaper and still would of had the same affect. If I was your assessor you would have got a bemused look from me as well :p:D

I said I would get all confused again.

Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
 
I said I would get all confused again.

Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?

Agree - this is the design flaw of the metal CU, that there are single insulated cables and connections inside an earthed metal box that only have the DNO fuse for protection, and if it's TT that won't melt real fast ... unless it's one of MY rod installs :rolleyes:
 
I said I would get all confused again.

Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?

That's why I use RCBO's on TT. Don't personally like the idea of unprotected single insulated conductors supplying the 30mA RCD's. I know we still have the busbar and tails to think about, but the busbar is solidly in place and the chances of that falling out is slim and if the tails are secured well so are they. But leesparkykent does have a good point about loosing the whole board in a N-E fault.
 
That's why I use RCBO's on TT. Don't personally like the idea of unprotected single insulated conductors supplying the 30mA RCD's. I know we still have the busbar and tails to think about, but the busbar is solidly in place and the chances of that falling out is slim and if the tails are secured well so are they. But leesparkykent does have a good point about loosing the whole board in a N-E fault.

The OSG gives guidance on TT supplies and use of RCBO's & RCD. Suitable use of glands would mitigate the tails shorting against the metal enclosure on entry. The issue with using RCD in such an enclosure, is the single insulated cable supplying each RCD, which may be damaged or pinched, and shorting with the metal enclosure. Using an up front S Type would provide fault protection in this case.

The issue with using SP RCBO's and upfront S Type, is in the case of a neutral-earth fault, is the S Type would eventually trip, but would then isolate the entire installation. Using dual RCD's, the same fault would only isolatate one half of the installation. Some guidance I received from my scheme Elecsa;

Good morning and thank you for your enquiry.

In regards To a TT and isolation of circuits regulation 537.2.1.1 must be taken into consideration. This regulation requires every circuit to be capable of being isolated from each of the supply conductors. (except in a TN-S or TNC-S)

This can be done various ways and it is permissible to isolate more than one circuit from a single device (GN2 section 4.3).

In the situation you describe with RCBO’s a double pole device will meet this requirement.

For further guidance refer to Guidance Notes 2 Isolation and Switching section 4 and the OSG as advised.

The diagram in the OSG that you mention (3.6.3.(iii)) is just one acceptable arrangement of RCD’s in a TT system. Other suitable arrangements are shown in 3.6.3.(ii) – (v).

It may be worth reading sections 2.2.5 & 2.2.6 (pages 20 & 21) in the OSG and also sections 3.6.1 – 3.6.3 (pages 30 – 32) and also section 3.6.3.4 on page 35 of the OSG.

It may also be worth reading regulation 531.4.1 & also regulation 537.1.2.

Some sections of BS7671 state the use of DP RCD’s, such as installations that fall under sections 705 & 708.
 
The OSG gives guidance on TT supplies and use of RCBO's & RCD. Suitable use of glands would mitigate the tails shorting against the metal enclosure on entry. The issue with using RCD in such an enclosure, is the single insulated cable supplying each RCD, which may be damaged or pinched, and shorting with the metal enclosure. Using an up front S Type would provide fault protection in this case.

The issue with using SP RCBO's and upfront S Type, is in the case of a neutral-earth fault, is the S Type would eventually trip, but would then isolate the entire installation. Using dual RCD's, the same fault would only isolatate one half of the installation. Some guidance I received from my scheme Elecsa;

Good morning and thank you for your enquiry.

In regards To a TT and isolation of circuits regulation 537.2.1.1 must be taken into consideration. This regulation requires every circuit to be capable of being isolated from each of the supply conductors. (except in a TN-S or TNC-S)

This can be done various ways and it is permissible to isolate more than one circuit from a single device (GN2 section 4.3).

In the situation you describe with RCBO’s a double pole device will meet this requirement.

For further guidance refer to Guidance Notes 2 Isolation and Switching section 4 and the OSG as advised.

The diagram in the OSG that you mention (3.6.3.(iii)) is just one acceptable arrangement of RCD’s in a TT system. Other suitable arrangements are shown in 3.6.3.(ii) – (v).

It may be worth reading sections 2.2.5 & 2.2.6 (pages 20 & 21) in the OSG and also sections 3.6.1 – 3.6.3 (pages 30 – 32) and also section 3.6.3.4 on page 35 of the OSG.

It may also be worth reading regulation 531.4.1 & also regulation 537.1.2.

Some sections of BS7671 state the use of DP RCD’s, such as installations that fall under sections 705 & 708.
BORING.BORING.
 
I said I would get all confused again.

Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
Yeah but the point I was making was the RCBO and upfront combo in the event of a neutral earth fault they would ending up loosing the lot as the up front RCD would still trip as the Wylex RCBO's are solid neutral. So it would be no different having a 30mA up front as you they would still loose the lot. That's why with TT its really RCBO's with no up front RCD or a dual RCD board with upfront RCD.
 
Yeah but the point I was making was the RCBO and upfront combo in the event of a neutral earth fault they would ending up loosing the lot as the up front RCD would still trip as the Wylex RCBO's are solid neutral. So it would be no different having a 30mA up front as you they would still loose the lot. That's why with TT its really RCBO's with no up front RCD or a dual RCD board with upfront RCD.

I did allude to that in my #54, perhaps it was too boring :)
 

Reply to Outbuilding on non RCD side of C/U? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains...
Replies
11
Views
3K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
890
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock