Discuss Outside building supply in the Australia area at ElectriciansForums.net

john f

-
Reaction score
0
Hello All

I am currently constructing a cattery 70 metres from our house
I will be running (if all on ) 5kw of heat lamps
I will also have a 32a ring main and of course lighting
My plan is to run 16mm swa from a henley block split from our house cu
The house is a TT earth (with incoming provision of PME)

The question is
Do I run 16mm swa twin core and use a earth spike at the cu in the cattery
or run a 3 core earthing both at the house cu and the cattery cu
the supply will not be using any of the ways from the house cu but will be split from the incoming to the house after the meter

John F


Read more: Outside building supply - DIYnot.com - DIY and Home Improvement
 
Not quite sure what you mean by house is a TT but incoming provision of PME? It's either one or the other unless someone has put an earth rod in for some other reason.
 
The house is TT and has a spike
The incoming from the supplier has PME sticker on fuse However the link has not been installed for the earth so the spike is the earth and is connected via 16mm single green yellow to the main earth terminal in the cu

john f
 
If I were you I'd get a registered sparks just to check your earthing arrangements - if your supplier is offering you PME then my advice would be to use it and save yourself a world of grief in other areas. Then, once using PME, run your supply (which is Part P notifiable in England/Wales) using a 3core SWA and take the earth with you ('exported PME').

There's a sticky on this forum about exporting PME to outbuildings so I won't go into it on this.
 
Hi John: Don't take this the wrong way but are you a Sparky & are you part P registered ?
If not then my advice would be to get 1 in.(Part P Sparky that is).
 
Last edited by a moderator:
First class answer
Without looking at the tables I,m sure as you say 16mm will have to have a fuse rated much lower

Thanks
John F

Just to let you know I did complete the 2360 installation course so I know enough to be dangerous yet my work is being checked by a "part P man"
thank god I hear you all say !

Regards
John F
 

Reply to Outside building supply in the Australia area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
962
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock