Discuss RCD keep tripping. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi All..
I have a 16mm 3 core swa feed a 9way split board in shed, 30m from incomer .. from the split board I have run a 10mm 3 core swa to 2 way board for hot tub. This has a 63amp rcd in it.. the other end at the split board is also a 63amp rcd on its own of one side of the split board.. this keeps tripping. The other side of the split board is on its own 63amp rcd and feed mcb for lights and sockets in shed. The hot tub is 3kw max . No cable faults or overload..Why does my rcd at split board keep tripping every few days? If fault was at Hottub would the 2way board rcd not trip? Should I ditch the split board RCD and swap with just a 40amp mcb? Thanks All
 
Last edited by a moderator:
This could turn out to be a N to earth fault somewhere.
Possibly water ingress into something.
 
2 rcd’s on the same line is not ideal. Can you remove one of them?

Both are 30mA, which means they’ll trip before the fault current reaches that threshold. so it’s the most sensitive of the 2 which is tripping, not the one closest to the tub.

Maybe the other rcd is faulty. Has it been tested with the test button?
 

Reply to RCD keep tripping. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
509
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock