One question i have had puzzling me for a while is if you use 2 core swa for a supply to a remote building with extraneous conductive parts and the armour is earthed at the supply end only (remote end made tt) and the cable is damaged towards the remote end ie fork through armour to phase conductor do we need to check the Zs phase to armour to ensure the protection will operate in the required time? long winded I know but do we need to ensure only volt drop and current carrying capacity are adequate for the cable and ignore R2 armour values????
 
You`d always take an R1+R2 at the extremity of a cct anyway - this would be no different...

Reading taken at end of armoured sub-main.

All beyond that is the TT subsystem.

& as stated, you can export the exponential zone, even for a TN-C-S if there are no extraneous-conductive parts at the location (a conventional shed wouldn`t `normally` have any) so perfectly acceptable in my view.

If there are Extraneous parts, bonding back to MET must be in minimum of 10mm, but as you`re `supposed` to aquire the DNOs permission anyway makes it suddenly less attractive.

TT it then...
 
You`d always take an R1+R2 at the extremity of a cct anyway - this would be no different...

Reading taken at end of armoured sub-main.

All beyond that is the TT subsystem.

& as stated, you can export the exponential zone, even for a TN-C-S if there are no extraneous-conductive parts at the location (a conventional shed wouldn`t `normally` have any) so perfectly acceptable in my view.

If there are Extraneous parts, bonding back to MET must be in minimum of 10mm, but as you`re `supposed` to aquire the DNOs permission anyway makes it suddenly less attractive.

TT it then...

I agree with all you say electricAl, however where do you get the DNOs permission bit.
 
The way i see it is if you export a PME earth, if the neutral becomes disconnected or damaged in the supply network, you have lost your earth to the outbuilding, which, if effect, is a higher risk area as it is outside the equipotential zone of the house.
 
That's true for a pme supply in general Jason. This is why the main protective conductor is sized in relation to the size of the neutral conductor with a minimum csa of 10mm.

Just re read your post Jason, the main problem is that if you lose your neutral, any equipotential bonding will carry the full load of the installation, this is why the mimimum csa for main protective bonding conductor is 10mm.
 
Last edited:
"an exposed conductive part connected to one means of earthing must not be simultaneously accessible with an exposed conductive part connected to another means of earthing" quote from wiring matters 2005 article referred to by Lenny- however, can't find this phrase in the 17th- where is it?

I can imagine, but haven't confirmed by testing, that a TT earth electrode installed at a garden shed may be at a different potential than a supply earth TNS at the house, so this sounds like a good idea, but 542.1.8 in the 17th and that section makes no mention of it, just stating that the protective conductor is to be only connected to one earth (and insulated from the other) if it is incapable of carrying the maximum fault current likely to flow.

Is this saying, as it seems to be, that it's ok to connect a TNS supplied earth to a TT earth electrode, so long as you have considered the current that may flow and rated accordingly?
 
That means that a 2 core 10mm swa whos armour is not sufficient sized for use as cpc would need to be 3 core and the third core connected to the insulated armours at the remote end and the MET at the supply end but not the remote installation EMB???? or am i missing something.
 

Reply to SWA 2 core or 3 core? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
718
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock