Discuss SWA cable rating - 2 core or 3 core? in the UK Electrical Forum area at ElectriciansForums.net

When calculating current carrying capacity of SWA; if you have 3 core swa but one core is being used as the cpc, is the SWA classed as 2 core?

If you use 3 core SWA for a single phase circuit, it won't dissipate as much heat as the same cable used for a 3 phase circuit running at the same current. I use the 'single phase' column values in the current carrying capacity tables.
 
I tend to judge it on the number of cores and not their function as more cores are likely to prevent heat dissipation. Some feel the third core used as a cpc is negligible.
 
I tend to judge it on the number of cores and not their function as more cores are likely to prevent heat dissipation. Some feel the third core used as a cpc is negligible.
If an extra core carrying no/negligible current made a significant difference to the heat dissipation, then there would be separate columns for 3 phase 3 core and 3 phase 4 core.
 
More warm cores (more phases) would slow heat dissipation. A cold core would increase the rate of heat loss.

Heat would be transferred from phase to colder cpc and out 'the other side', dissipating it quicker. If all the cores were warm to begin in with you wouldn't get heat transfer as they are all warm.

I guess this is why I'm here discussing it.
 
If an extra core carrying no/negligible current made a significant difference to the heat dissipation, then there would be separate columns for 3 phase 3 core and 3 phase 4 core.
Possibly but it is interesting that YY, CY and SY cables give a ccc for the conductor csa and then you apply correction factors for core quantity with no relevance to core function.
 
YY, CY, and SY wont be found in BS7671 as they aren't recognised.
I know, I just find it interesting. I think the Tables in BS7671 are bound in the past with regards to conductor function above two core.
 
Possibly but it is interesting that YY, CY and SY cables give a ccc for the conductor csa and then you apply correction factors for core quantity with no relevance to core function.
I guess the values are calculated on worst case scenarios, i.e on the assumption that all cores have to be considered as load current carrying.
 
Comparing 2-core and 3-core cable with two cores loaded, there are two thermal factors at work. The greater outside diameter of the 3-core increases the surface area in contact with air, which is usually the main barrier to heat dissipation, so the 3-core can dissipate more heat in total. On the other hand the internal construction determines how well heat can flow from the two loaded cores to the outside - I would expect this effect to be much less significant, although if it is a rope-wormed cable rather than extruded solid or sectored, the air pockets might have an effect. Overall, I would expect a 3-core cable to be as good or bettter than 2-core so I use the 2-core figures.

In contrast, a 3-core cable for a 3-phase circuit could have all three cores loaded so the dissipation could be 50% greater. Since the surface area cannot increase by more than the square root of the CSA, and in practice increases less, the CCC must be lower than for a 2-core. This is why I would not apply the 3-core 3-wire 3-phase tabulated rating to a single-phase circuit. The difference between a 3-phase 3-wire and 3-phase 4-wire is less significant. The difference between the cable O/D's is less, and although the heat dissipation is likely to be lower (without harmonics, sharing some current with the neutral decreases the sum of I²R values of the separate cores) there is the possibility of harmonics increasing the dissipation above the 3-core value for the same RMS total load.

This difference is why I would use different figures for 2- and 3-core cables used for a single-phase circuit, but the same figures for a 3- or 4-core cable used for a 3-phase circuit.

The unusual case mentioned above, of a 3-core cable used for L1, L2 and N would seem to fall into the 3-phase scenario.
 

Reply to SWA cable rating - 2 core or 3 core? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was the 2nd sparks taking over a garden office supply job. The first sparks had fitted 10 sq mm 3 core SWA, but it actually had brown, blue and...
Replies
5
Views
812
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
465
Does anyone know what the cable in the picture is called? Or anything about it? Labelling on the outside is “E SPC Electric Cable 600/1000v” Its...
Replies
9
Views
1K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
387
Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable...
Replies
2
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock