Discuss SWA size. 6mm ok or 10mm needed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Hi guys,

any advice on what size of SWA should be burried for garage? Will be aprrox 15m long. Garage will have 6A lighting circuit 20A socket circuit and 32A power socket. Idealy 2core SWA as only one phase needed. IS 6mm ok or 10mm needed?

THX.
 
Welcome to the forum mate.

If you answer the questions in post #2 then we can help you out more, maybe.
Also be aware of post #3 comment regarding Part P.
 
No there are not. Design load of maximum 58A that means 13.34KW. OCPD 60947-3 probably 80amp as main switch (in the house) and then RCDo 63amp in mcb in garage.

By my calculations 10mm would be better. Correct?

Quite a worrying response here. OCPD for the garage supply is the house CU main switch ?

As you are a new member could you state what qualification and experience you have, or pop it on your profile and set your profile to be able to be viewed publicly. This will help us help you best.
 
No there are not. Design load of maximum 58A that means 13.34KW. OCPD 60947-3 probably 80amp as main switch (in the house) and then RCDo 63amp in mcb in garage.

By my calculations 10mm would be better. Correct?

I didn’t think 60947-3 related to OCPDs, but I may be wrong.

Do you mean you are intending to use an 80A OCPD? In which case I don’t think 10mm will be suitable, off the top of my head 16mm may be better.
 

Reply to SWA size. 6mm ok or 10mm needed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
644
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
475
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
818
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock