Can somebody explain if you had a 230v to earth fault the variables that determine touch voltage of a person to earth and is this voltage less the closer you get to the MET of an installation.

Thanks guys
 
Can somebody explain if you had a 230v to earth fault the variables that determine touch voltage of a person to earth and is this voltage less the closer you get to the MET of an installation.

Thanks guys
Well if the line to earth fault takes place in a TNC-S system (the one I am most familiar with) then you are correct in assuming that the closer you get to the MET then the smaller the touch voltage will be.
The basic variables that will determine the touch voltage to earth will be the point of resistance along the new circuit that has been formed by the short, that a person physically comes into contact with.
 
max touch voltage at any point of Installation is 50v

Regs book is in van and its ----ing down at moment.

the touch voltage is linked to max currant a human body can take before its considered fatal.
it works out about 1667 Ohms of resistance for a human.
1667Ohms is also max Zs for a 30ma RCBO.
 
max touch voltage at any point of Installation is 50v

Regs book is in van and its ----ing down at moment.

the touch voltage is linked to max currant a human body can take before its considered fatal.
it works out about 1667 Ohms of resistance for a human.
1667Ohms is also max Zs for a 30ma RCBO.
Yes. You are correct regarding the max touch voltage not been over 50v.But I u derstood the OP question was in relation to the "variables" that would determine this voltage. Hope the "-----" has stopped
 
Jako its Ohms law.
Yes. You are correct regarding the max touch voltage not been over 50v.But I u derstood the OP question was in relation to the "variables" that would determine this voltage. Hope the "-----" has stopped


max is always 50V no change between end of final circuit and metal main Distribution board over 50V could be fatel.
 
During a fault you will get the supply volts times R2/(R1+R2) relative to true Earth where R1 includes the supply phase impedance, and R2 includes the supply ground.

But it is complicated by the other aspects such as any water/gas bonding to metallic pipes that might raise the local earth where you are standing up a bit relative to true Earth.

So you can see voltages from around 1/2 supply (on long supply cable with R1 around R2) to close to the supply (if R2 is very high on TT system). But the danger of serious impact also depends on the exposure time, hence the values of 0.4s (typical LV TN-S) and 0.2s (TT) for max disconnection to try and keep the likely current-time exposure down.

If you are unfortnuate enough to be in good contact, say a swimming pool , then the current can be much higher even though a similar disconnection time is likely. Hence the requirement for SELV in that sort of high risk area as an RCD limits the exposure time, not the actual current, you might get.
 
During a fault you will get the supply volts times R2/(R1+R2) relative to true Earth where R1 includes the supply phase impedance, and R2 includes the supply ground.

But it is complicated by the other aspects such as any water/gas bonding to metallic pipes that might raise the local earth where you are standing up a bit relative to true Earth.

So you can see voltages from around 1/2 supply (on long supply cable with R1 around R2) to close to the supply (if R2 is very high on TT system). But the danger of serious impact also depends on the exposure time, hence the values of 0.4s (typical LV TN-S) and 0.2s (TT) for max disconnection to try and keep the likely current-time exposure down.

If you are unfortnuate enough to be in good contact, say a swimming pool , then the current can be much higher even though a similar disconnection time is likely. Hence the requirement for SELV in that sort of high risk area as an RCD limits the exposure time, not the actual current, you might get.

Isn’t R2 the CPC of the final circuit measurement. The main earth readings. On TNC-S and TT are linked in relation to disconnection times PFC etc but not measured as an R2
 
Isn’t R2 the CPC of the final circuit measurement.
Yes, that is the normal convention, which is why I put in the comments about it being the earth return to the source (i.e. local CPC and supply ground combined). Same for R1 being the impedance to the source (local circuit R1 plus supply phase R1).

Basically R2/(R1 + R2) is your classic voltage divider / potentiometer.

The Ze value has both supply phase and supply ground combined but you don't know in what ratio (i.e. is supply R1 similar to supply R2 so both around Ze/2 or not). Though in the TT case the supply is so much less than most rod's Ra values it can largely be ignored. The DB Zs would have any supplementary bonding of service pipes included so normally is less by a small amount (supply R2 having multiple paths back to the source / true Earth).

How much less depends on the extraneous part's path to Earth. In my of flat's case it is noticable as they are shared with other flat's bonding to the supply earth, hence my DB's Ze is 0.19 ohm and Zs 0.16 ohm (84% of Ze so 19% higher PFC).
[automerge]1599988359[/automerge]
See this attachment for the long answer...
That has all of the details and the impact of the extraneous part bonding covered as well. Well done for finding that document!
 
Last edited:
During a fault you will get the supply volts times R2/(R1+R2) relative to true Earth where R1 includes the supply phase impedance, and R2 includes the supply ground.

But it is complicated by the other aspects such as any water/gas bonding to metallic pipes that might raise the local earth where you are standing up a bit relative to true Earth.

So you can see voltages from around 1/2 supply (on long supply cable with R1 around R2) to close to the supply (if R2 is very high on TT system). But the danger of serious impact also depends on the exposure time, hence the values of 0.4s (typical LV TN-S) and 0.2s (TT) for max disconnection to try and keep the likely current-time exposure down.

If you are unfortnuate enough to be in good contact, say a swimming pool , then the current can be much higher even though a similar disconnection time is likely. Hence the requirement for SELV in that sort of high risk area as an RCD limits the exposure time, not the actual current, you might get.
So basically it’s the difference between the raised voltage of the installation when the fault occurs the the true earth we may be standing on that determines the voltage?
 

Reply to Touch voltage to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi everyone I asked my assessor about touch voltage and he was not keen on explaining properly and gave me a rough answer which made me think...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock