Discuss Touch voltage to earth in the UK Electrical Forum area at ElectriciansForums.net
Well if the line to earth fault takes place in a TNC-S system (the one I am most familiar with) then you are correct in assuming that the closer you get to the MET then the smaller the touch voltage will be.Can somebody explain if you had a 230v to earth fault the variables that determine touch voltage of a person to earth and is this voltage less the closer you get to the MET of an installation.
Thanks guys
Yes. You are correct regarding the max touch voltage not been over 50v.But I u derstood the OP question was in relation to the "variables" that would determine this voltage. Hope the "-----" has stoppedmax touch voltage at any point of Installation is 50v
Regs book is in van and its ----ing down at moment.
the touch voltage is linked to max currant a human body can take before its considered fatal.
it works out about 1667 Ohms of resistance for a human.
1667Ohms is also max Zs for a 30ma RCBO.
Yes. You are correct regarding the max touch voltage not been over 50v.But I u derstood the OP question was in relation to the "variables" that would determine this voltage. Hope the "-----" has stopped
During a fault you will get the supply volts times R2/(R1+R2) relative to true Earth where R1 includes the supply phase impedance, and R2 includes the supply ground.
But it is complicated by the other aspects such as any water/gas bonding to metallic pipes that might raise the local earth where you are standing up a bit relative to true Earth.
So you can see voltages from around 1/2 supply (on long supply cable with R1 around R2) to close to the supply (if R2 is very high on TT system). But the danger of serious impact also depends on the exposure time, hence the values of 0.4s (typical LV TN-S) and 0.2s (TT) for max disconnection to try and keep the likely current-time exposure down.
If you are unfortnuate enough to be in good contact, say a swimming pool , then the current can be much higher even though a similar disconnection time is likely. Hence the requirement for SELV in that sort of high risk area as an RCD limits the exposure time, not the actual current, you might get.
Yes, that is the normal convention, which is why I put in the comments about it being the earth return to the source (i.e. local CPC and supply ground combined). Same for R1 being the impedance to the source (local circuit R1 plus supply phase R1).Isn’t R2 the CPC of the final circuit measurement.
That has all of the details and the impact of the extraneous part bonding covered as well. Well done for finding that document!See this attachment for the long answer...
HELP!! Attachment wont download for me. Any advice very welcome.See this attachment for the long answer...
Still works for me (Firefox on Linux PC), but I expect any desktop should work. Are you using a phone to view things?HELP!! Attachment wont download for me. Any advice very welcome.
Tablet. But I will give the desktop a go. Thanks ?Still works for me (Firefox on Linux PC), but I expect any desktop should work. Are you using a phone to view things?
Yes. It kept saying download failed but I will take pc1966 advice. Thank youIt’ll have ended up in some “downloads” folder somewhere. You got to go look for it.
So basically it’s the difference between the raised voltage of the installation when the fault occurs the the true earth we may be standing on that determines the voltage?During a fault you will get the supply volts times R2/(R1+R2) relative to true Earth where R1 includes the supply phase impedance, and R2 includes the supply ground.
But it is complicated by the other aspects such as any water/gas bonding to metallic pipes that might raise the local earth where you are standing up a bit relative to true Earth.
So you can see voltages from around 1/2 supply (on long supply cable with R1 around R2) to close to the supply (if R2 is very high on TT system). But the danger of serious impact also depends on the exposure time, hence the values of 0.4s (typical LV TN-S) and 0.2s (TT) for max disconnection to try and keep the likely current-time exposure down.
If you are unfortnuate enough to be in good contact, say a swimming pool , then the current can be much higher even though a similar disconnection time is likely. Hence the requirement for SELV in that sort of high risk area as an RCD limits the exposure time, not the actual current, you might get.
Can anyone give me the name on this link. Can't download it for some reason so hoping to just Google it?See this attachment for the long answer...
https://onlinelibrary.wiley.com/doi/pdf/10.1002/9781444324273.app01Can anyone give me the name on this link. Can't download it for some reason so hoping to just Google it?
My advice is leave it at that! Reading it will give you a headache )Any advice very welcome.
The advance warning is much appreciated?My advice is leave it at that! Reading it will give you a headache )
By the way, one of your comments sometime ago about "Earthing and bonding been one of the most confusing topics" you have experienced came to my mind last night in relation to several electrical forums I, ve been dipping in to. Its seems to be an ongoing issue within the industryThe advance warning is much appreciated?
Reply to Touch voltage to earth in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.