Discuss two inverters connected separate or parallel in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

E

erf151an001

I have two inverters wired to two strings. Do I need two separate wires from each inverter to an individual mcb. Or can I dual up the supply so only using 1 isolator at the generation meter end. I will still have 2 isolators in the loft adjacent each inverter. Or is it best practice to run 2 separate circuits? Although they will be connected together at the generation meter anyway. Your thoughts ate welcome?
 
I suspect it depends on the inverter. The SMA ones I have installed have all stated in the manufacturers instructions that they should be on a separate mcb. What do the installation instrs say?
Regards
Bruce
 
thanks for the replies guys.

I can see that ideally you would supply each invereter via separate mcb's but unless I'm missing something, if for instance the mcb were to trip for inverter 1.

Being as the supplies are common in the generation meter it would still have a supply via the mcb for inverter 2.

I assume its not normal to install a generation meter per inverter?

No mention in the manufacturers instructions either!

They are Solar Europa 1500 inverters.

Think its easier to install via 1 mcb and 1 isolator downstairs next to the generation meter then this supply will be wired to each isolator in the loft adjacent each inverter.

Need to get this right as its the install I'm using for my MCS accreditation.

Any more thoughts?
 

Reply to two inverters connected separate or parallel in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Hi all, I am shortly installing 2 x 5kw Huawei sun2000 L1 =(1ph) inverters along with a new generation meter but unsure how I connect the...
Replies
0
Views
546
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
432

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock