You most likely find that the inverter is creating "noise" on the circuit and therefore not allowing you to carry out the test.

If the unit is plugged into a 32amp commando then just unplug it, or if through an isolator switch it off.

If it's hard wire direct, then just disconnect at the board and test the RCBO/RCD at source
 
I have been testing directly out of the rcd/rcbo but it is not tripping. What earthing arrange should the inverter have?

Yes ok you have been testing at the CU, but as I said did you have the inverter/charger disconnected ? What earthing arrangement do you have at the site?

None of them that is. Not sure about the inverter?

​None of them? None of them what?


 
Not sure what setup you've got specifically but the Victron inverters are high end equipment. We've fitted several of their inverters in marine and onshore applications and we've never had problems with them. They are a very well thought out product which is scalable in all directions, you can even use three of their single phase inverters and link them together to make a 3-phase 400v output. As far as I know all their products are pure sine output so I doubt it's a noise issue as previously suggested. I would be looking at the way the earthing arrangement was installed.
 

Reply to Victron Multiplus inverters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am doing a campervan conversion and have a 16A/250V shore power connection coming into a consumer unit which has two breakers - one for the AC...
Replies
8
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
Hi, agricultural off grid project, Victron inverter/charger, BYD LVS and Pramac GBW22P generator. The generator has a DSE4520 controller...
Replies
0
Views
218
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi there, anyone had any experience with the generation 3 inverter I'm having problems connecting to the hotspot feature. Thanks
Replies
1
Views
264

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock