Discuss Will a 10mm PYRO take 80 amps ? in the Australia area at ElectriciansForums.net

S

sycamore89

Hi,

I need to change the main incoming fuse from 60A to 80A but there is a 10mm pyro feeding the property and i dont really want to replace this. The reason I need to up the supply to 80A as I am installing a sunbed which runs at 40A single phase. The load will never constantly be running at 80A so thought that the 10mm pyro would be sufficent.

Property has 2 rings with only a few computers and hairdryers etc.... has no oven but 1 microwave so not much load on any other circuits.

Would this be ok ?
 
As with most things of this nature, it very much depends on the reference method used for installation. Some allow higher than 80A, some don't.

But you shouldn't be messing about with the main fuse anyway, that's a job for the DNO.
 
Last edited by a moderator:
WHY are YOU changing the DNO fuse? WHY have you pulled the DNO fuse ? Have you asked the DNO if their supply cable can take the rise in loading? Are you an electrician ?
 
I have not pulled the DNO fuse yet but I will do for safe isolation while I change the cu! Property is fed by a 25mm SWA! And no I'm not a sparks I'm a plumber !!!
 
I have not pulled the DNO fuse yet but I will do for safe isolation while I change the cu! Property is fed by a 25mm SWA! And no I'm not a sparks I'm a plumber !!!

so WTF are you attempting a procedure that is illegal for qualified sparks to do, let alone a wet-head
 
The property in question is obviously a commercial one, and will consequently not be covered by part pee. Therefore if the owner thinks its ok to employ a plumber to do electrical work, then that is their problem. Can't see the insurance paying out when it burns down though :devilish:
 
IF you ahvent yet pulled the fuse HOW do you know its rated at 60a ?? as telex said what your proposing is ILLEGAL and this is an OPEN forum
 
If it says 60 on the outside then it will only take 60 MAX DNO will need to upgrade cutout as cutout is rated at 60a the fuse might only be a 40 CALL THE DNO this job cant be done by a spark never mind a 6 week plumber as for your changing the C.U I trust your client will be having the cert delivered by post filled in by joebloggs?
 

Reply to Will a 10mm PYRO take 80 amps ? in the Australia area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
215
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
487
Hello Guys Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven. I've looked at...
Replies
4
Views
1K
Howdy All, just after a 2nd opinion as i'm doubting myself. I went to a property to look at replacing the ccu, I noticed what I thought was a...
Replies
17
Views
2K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock