Evening all, apologies if this is in the wrong forum or has been asked before.
I have ordered a new oven thinking I could just plug it in to 13amp socket same as my old one. However I checked today and the oven is 16amp and therefore should have its own dedicated circuit.
I checked the instructions for the old oven and turns out that is also 16amp, however it has been connected to 13amp socket.
I understand that using 3 core flex to connect the new oven to a 3 pin socket does not conform to regulations, and I do not intend on doing so.
But if the plug was fitted with 13amp fuse, would this not adequately protect the cable from over current? Assuming the oven was at full load and drawing 16amps, would the plug top fuse simply blow causing a minor annoyance at dinner parties?
I must stress again that I have no intention on doing it this way, I just have a keen interest in electrical theory and want to know for my own satisfaction
Thanks in advance
Beeg
I have ordered a new oven thinking I could just plug it in to 13amp socket same as my old one. However I checked today and the oven is 16amp and therefore should have its own dedicated circuit.
I checked the instructions for the old oven and turns out that is also 16amp, however it has been connected to 13amp socket.
I understand that using 3 core flex to connect the new oven to a 3 pin socket does not conform to regulations, and I do not intend on doing so.
But if the plug was fitted with 13amp fuse, would this not adequately protect the cable from over current? Assuming the oven was at full load and drawing 16amps, would the plug top fuse simply blow causing a minor annoyance at dinner parties?
I must stress again that I have no intention on doing it this way, I just have a keen interest in electrical theory and want to know for my own satisfaction
Thanks in advance