Discuss 16A 4 pin wall socket in the Canada area at ElectriciansForums.net

B

bikeman

This is my first post so Hi to all

I have to wire in a couple of 16 amp 3 phase wall sockets in a work shop.
The ones I have been given are 4 pin.

If I run Line 1, Line 2, and Line 3 standard brown Black Grey I am guessing the 4th pin is for earth and power is between each phase?

Just checking as I have this naggin doubt that the 4th pin would be for neutral.

I have to install 2 in the work shop and there is a spare 20A 3Phase CB on the board I am guessing I can ring each line back to the board?

Thanks for any responce
 
Sounds like a 3 phase supply for a motor no neutral needed. So yes L1 L2 L3 & cpc.

I personally would not wire these on a ring. I would run in a seperate radial for each 4 pin back to seperate MCB's.
 
as above and you also need to think of motor protection methods, you dont want somebody to test a 1kw motor using a socket on a 20amp beaker
 

Reply to 16A 4 pin wall socket in the Canada area at ElectriciansForums.net

Similar Threads

I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
753
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
674
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
818
Hi, leading on from my question the other day about running the 3 phase compressor off my 8.5kW generator I have since got my hands on a 240v to 3...
Replies
0
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock