Search the forum,

Discuss 3 core - what colour do you use as a switch wire? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Black as well, because it's in the middle, so you can easily cut the strappers on either side and leave the black unbroken if you want to, for an intermediate switch
 
Grey - because I equate black with neutral in the old colours (and still prefer to use it as such if a neutral is required), and I equate brown with permanent live.
 
Recommendations are to use grey as sleeved neutral now (how I do it), in order to get us away from thinking of black that way. Not critical though, just as long as they are sleeved at both ends.
 
BROWN = Permanent Live

BLACK = Switched Live where Required or Strapper 1 on two way circuits (Sleeved with a section of Brown over-sleeve)

GREY = Neutral where required or Strapper 2 on two way circuits. (Sleeved with a section of Black/Brown over-sleeve as appropriate)

Where a 3 core is used on a single phase circuit (not necessarily lighting)

BROWN = LIVE

GREY = NEUTRAL

BLACK = CPC (Sleeved Green/Yellow)

 
as above. use grey as N is standard practice to disassociate the black from neutral, thanks to the meddling of johnny foreigner. as for 2 way switching, back in the days of sensible cable colours, most of us used the yellow for common and R/B for strappers so that in the switch with the switch wire from the light, you has red with red and blue with black. this equates to black for yellow, brown for red and grey for black
 
as above. use grey as N is standard practice to disassociate the black from neutral, thanks to the meddling of johnny foreigner. as for 2 way switching, back in the days of sensible cable colours, most of us used the yellow for common and R/B for strappers so that in the switch with the switch wire from the light, you has red with red and blue with black. this equates to black for yellow, brown for red and grey for black
down here we used the red as common, sometimes come across the yellow used as it but not much
 
not where i've been. generally yellow for common.
 
not where i've been. generally yellow for common. but then most of us knew that the blue wasn't neutral in 2 way switching. not like some of these young sprogs today.
 
something to do with the water in yorkshire. we only allow what we don't want to blow over the ridge.
 
I had heard that the reason for harmonisation was to get
away from red being used as it is classed as a 'Dangerous' colour, it clearly worked as now every Tom, Dick and Harry thinks they can do electrics.
Still black as switch, grey as neutral.
 
as msg 6. any other way is a deviation. grey is the old black. im sure its wrighten somwhere.. but im on the beer again, and the chance of finding the page is as good as zero
 
Ah, this old chestnut.

Black (sleeved brown) as permanent live, because that's how flex 7, rock etc flexes come pre-wired, and because you use brown as switched live everywhere else where you haven't got a permanent live so it keeps it consistent.
Brown as switched live as you usually would if there weren't a permanent live.
Grey (sleeved blue) as neutral.

Also because 4 core flex comes with brown, black, blue, and green & yellow.
Black as Auxiliary live.

Brown as L1 with the feed (also brown) so browns go together.
Grey as L2 (sleeved brown) with the switched live (blue, sleeved brown)
Black (sleeved brown) because it's the other one.
 
Last edited by a moderator:
Was told at time of harmonisation to get away from using black as neutral we had to "deneutralise the black" if that's even a word!!
 
when doing em and normal lighting mixed, it's usually black (sleeved) for perm., brown for switched.
 
Brown permanent live.
black switch line.
grey switch linear neutral.
harmonisation did state not to use back as neutral any more so that it did not get confused with old black neutrals therefore you had in old 3 phase boards black and greys as neutrals. That wouldn't confuse any body would it.
also I was taught on a 2way switch if you follow the circuit through the switch in the off position then the grey would actually be a neutral.
check it out it s true via the lamp
 
"harmonisation" did state not to use back as neutral any more !!!

Did he..............where?
Is this harmony guy still on the tools...........so to speak?

And I take it you meant black not back:)
 
Brown permanent live.
black switch line.
grey switch linear neutral.
harmonisation did state not to use back as neutral any more so that it did not get confused with old black neutrals therefore you had in old 3 phase boards black and greys as neutrals. That wouldn't confuse any body would it.
also I was taught on a 2way switch if you follow the circuit through the switch in the off position then the grey would actually be a neutral.
check it out it s true via the lamp

how can grey be a neutral in 2 way switching when they're all live or switched live?
 
Ah, this old chestnut.

Black (sleeved brown) as permanent live, because that's how flex 7, rock etc flexes come pre-wired, and because you use brown as switched live everywhere else where you haven't got a permanent live so it keeps it consistent.
Brown as switched live as you usually would if there weren't a permanent live.
Grey (sleeved blue) as neutral.

Also because 4 core flex comes with brown, black, blue, and green & yellow.
Black as Auxiliary live.

Brown as L1 with the feed (also brown) so browns go together.
Grey as L2 (sleeved brown) with the switched live (blue, sleeved brown)
Black (sleeved brown) because it's the other one.

exactly. greg flexes come pre-wired in that exact way. so black as perm L.
 
how can grey be a neutral in 2 way switching when they're all live or switched live?

Draw out the circuit including the lamp. Back trace the neutral through the lamp to the switch and when the switch is off the grey is connected to neutral. Image the lamp s a link not a load.
i know it's barmey but in some weird way it makes sense lol
 
So who can come up with any kind of argument for using black as switched live and brown as permanent, other than 'that's what you do'?
 
Check out posts #3 & #5

Ahhh but your missing the whole point thomas .......if you don't mind me saying.
As long as it's sleeved the same colour (at both ends) it won't be a black anymore..........it'll be blue if used as a neutral:)

As poster #3, of course I sleeve a neutral with blue, and a switched live with brown - and at both ends!

I checked my BS7671 and OSG, there didn't seem to be anything I could find to say it was wrong to be using the black in a 3-core brown/grey/black cable for neutral, so long as it is sleeved blue. Not sure if various bits of guidance around the time of the change over suggesting we should not do this carry any weight. But I'm happy to change if someone can point out a regulation or best practice I've overlooked.
 
Ah, this old chestnut.

Black (sleeved brown) as permanent live, because that's how flex 7, rock etc flexes come pre-wired, and because you use brown as switched live everywhere else where you haven't got a permanent live so it keeps it consistent.
Brown as switched live as you usually would if there weren't a permanent live.
Grey (sleeved blue) as neutral.

Also because 4 core flex comes with brown, black, blue, and green & yellow.
Black as Auxiliary live.

Brown as L1 with the feed (also brown) so browns go together.
Grey as L2 (sleeved brown) with the switched live (blue, sleeved brown)
Black (sleeved brown) because it's the other one.

Going to say that myself as when you get pre wired kliks/gregs the black is normally the permanent live
 
As poster #3, of course I sleeve a neutral with blue, and a switched live with brown - and at both ends!

I checked my BS7671 and OSG, there didn't seem to be anything I could find to say it was wrong to be using the black in a 3-core brown/grey/black cable for neutral, so long as it is sleeved blue. Not sure if various bits of guidance around the time of the change over suggesting we should not do this carry any weight. But I'm happy to change if someone can point out a regulation or best practice I've overlooked.

My sentiments exactly mate :)
 
Interesting point - surely black and grey, if used as strappers, dont need to be sleeved or taped brown as they are two of the possible three 'live' colours?!?! Is this wrong?!
 
Interesting point - surely black and grey, if used as strappers, dont need to be sleeved or taped brown as they are two of the possible three 'live' colours?!?! Is this wrong?!

used to have same argument with red/yellow/blue. general opinion was treat any cable as live unless proved otherwise. sadly common sense is out the window these days, and we have to allow for idiots.
 
I'm with you but grey black brown are ALL BS7671 LIVE colours. Ok as strappers they are not three phase l1 l2 l3 but they are live colours. Not 'any colours' if you see what i mean mate.
 
In the end it falls into good practice and again shows the lack of clear definition in the regs. I don't see any issue with anyone using black or brown for permanent live, my personal choice is brown for perm, black for switched.
Where the lack of guidance shows up is on big sites with multiple sparks working on the same installation. It means that rather than being able to just get in and do the job, you are going around asking the colour codes that they have been using.
For example, I had to go around and fit some timer switches, all other accessories wired and fixed back so no visible wiring Barr for the cable I was to terminate, a three core. I spoke to the spark on site who informed me that brown was permanent live. I therefore went and terminated all 300 switches with brown as permanent. When it came to energisation it became apparent that 200 or so weren't working, the reason, another spark, now on holiday, had been on site and wired black as perm as this was what he always did, this obviously unknown until so many didn't work, thus a lot more work created putting right.
I understand we use sleeving to identify wiring, however we should also have a standard set as to what we use for perm or switch, neutral, etc, so that confusion is to a minimum.
 
In the end it falls into good practice and again shows the lack of clear definition in the regs. I don't see any issue with anyone using black or brown for permanent live, my personal choice is brown for perm, black for switched.
Where the lack of guidance shows up is on big sites with multiple sparks working on the same installation. It means that rather than being able to just get in and do the job, you are going around asking the colour codes that they have been using.
For example, I had to go around and fit some timer switches, all other accessories wired and fixed back so no visible wiring Barr for the cable I was to terminate, a three core. I spoke to the spark on site who informed me that brown was permanent live. I therefore went and terminated all 300 switches with brown as permanent. When it came to energisation it became apparent that 200 or so weren't working, the reason, another spark, now on holiday, had been on site and wired black as perm as this was what he always did, this obviously unknown until so many didn't work, thus a lot more work created putting right.
I understand we use sleeving to identify wiring, however we should also have a standard set as to what we use for perm or switch, neutral, etc, so that confusion is to a minimum.

My word, that would be well annoying!! I use brown perm and black switched. And then grey to link the commons.
 
Good job they don't "have a guess" at 5/10/20 pair or more Blue instrument cables I've seen that done where a so called spark makes his own colour code up on a site, caused many a problem at commissioning time lol
 
I cannot believe that my apprentices tutor at college (Leeds college of Building) is actually teaching his students to use black as neutral with a blue sleeve and grey for switched wire or strapper in a 3 core cable 2-way circuit.

He is adamant he is right and my apprentice is worried he will fail his exam as I have told him I NEVER want to see a black wire used as a neutral in any of our work.....EVER!

There is no sense in this at all.
 

Reply to 3 core - what colour do you use as a switch wire? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm trying to wire in a 4 core capacitive sensor into a safety circuit. I have brown, blue, white and black coloured cores and it's a NO sensor...
Replies
1
Views
252
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
1K
Hi, I'm replacing a light fitting in the bathroom but the wiring is confusing me, black brown and grey? Is black neutral and brown live in this...
Replies
14
Views
2K
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock