Discuss 3 phases at 600 modular !,, in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

SP4RKI

-
Reaction score
1
Hi all, doing an IECR all the lights are via contactors, 2 X lamps on one circuit L1 --- 2 X lamps on another circuit L2 ---- and the permanent feed on another supply L3 ---

Would you you fail this installation?

would a simple label in the light saying isolate from more than one mcb be sufficient



Thansk ink in advance
 
Are you trying to say that the lights have 3 different phases at them, 1 phase for 2 lamps, 1 phase for the other two lamps and 1 phase for the perm feed?
4 lamps per light
 
Strange imo. Were the lights modified to allow this, extra control gear installed.
Just thinking why would this be done, where are they installed?
400v stickers and the relevant isolation stickers at the DB and in the fittings should be sufficient.
 
Absolutely positive are you? can't quite work out yet how that would work, without being modified in some way, you would have a very badly designed phase loading situation IMO
 
Last edited:
On older fire stations you sometimes get this setup but the fittings are definitely modified with extra ballasts.
L1 turns on two tubes via wall switch.
L2 turns on two tubes via a contactor when station is mobilised.
L3 used for the EM aspect of some fittings.
 
Surely that could all be done via one supply. 3 separate supplies at one light fitting seems dodgy to me....400v and 3 separate phases sounds like a bit of a death trap. Two switch wires and a permanent L would do the job.
 
Last edited:
To be fair all you have to do isolate the supply to the coil and the equipment will be dead.

Are you allowed under safe isolation to rely on a contactor for safe isolation, don't think so, lockable isolators spring to mind
 
Was pointing out that there was no need to isolate multiple circuits to work on the lights, only the control circuit to the coil. It should of course be done safely but thats down to the person whos going to work on the circuit.
 
Was pointing out that there was no need to isolate multiple circuits to work on the lights, only the control circuit to the coil. It should of course be done safely but thats down to the person whos going to work on the circuit.

Sorry yes there is a need to isolate all the circuits.
 

Reply to 3 phases at 600 modular !,, in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
465
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
686
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
714
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
875
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top