Discuss 3x230 in the Industrial Electricians' Talk area at ElectriciansForums.net

Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?
When you say 'system' is the building supply 2 phases as you describe without a neutral or is this just a final circuit.

Either way the answer is yes in most places on the planet (including Derbyshire....wherever it may be), you'd need every point of consumption including light fittings to be supplied by a double pole switch.

I think England is in Derbyshire and Derbyshire is part of the UK, but I might be wrong :).
 
Last edited:
Since 133V isn't a normal supply voltage, SP loads would all have to be connected L-L and for practical purposes it would be used as a delta supply. Whilst delta power is common for certain applications, e.g. shipboard, it can make things a lot harder. All switching and OCP must be DP, so you can't use 13A plugs for example.

Illegal - no, but not terribly useful for most applications and a general purpose electrical installation fed that way might be considered unfit for purpose.
 
Since 133V isn't a normal supply voltage, SP loads would all have to be connected L-L and for practical purposes it would be used as a delta supply. Whilst delta power is common for certain applications, e.g. shipboard, it can make things a lot harder. All switching and OCP must be DP, so you can't use 13A plugs for example.

All loads are indeed connected L-L with 2 pole MCBs used on all circuits.

The switching I am unsure about. Would lights still need DP switching?

Illegal - no, but not terribly useful for most applications and a general purpose electrical installation fed that way might be considered unfit for purpose.

Sounds like a lot of draw backs. Is switching on of them?
 
When you say 'system' is the building supply 2 phases as you describe without a neutral or is this just a final circuit.

Either way the answer is yes in most places on the planet (including Derbyshire....wherever it may be), you'd need every point of consumption including light fittings to be supplied by a double pole switch.

I think England is in Derbyshire and Derbyshire is part of the UK, but I might be wrong :).

Building supply and final circuit. 4 conductors (3 phases and a PE)

What part of the regs require 2 pole switches for lights?
 
Yes, lights would need DP switching otherwise the lampholder would still be live w.r.t. earth with the switch off.
 
You pull the plug out! BTW, the very reason that Schuko isn't polarised, is that this method of supply was once used in Germany, and there was no advantage polarising the connector when both sides were lines. But that was phased out (see what I did there?) in favour of ordinary star 230/400.
 
You pull the plug out! BTW, the very reason that Schuko isn't polarised, is that this method of supply was once used in Germany, and there was no advantage polarising the connector when both sides were lines. But that was phased out (see what I did there?) in favour of ordinary star 230/400.

But if its ok for a table lamp, why would it be different for a light fitting? Unless the socket is designed to denergize the screw shell when removing the bulb?

Double pole switches would be easy, but 2 way switches would be a challenge.
 

Reply to 3x230 in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I have a lighting circuit cable (1mm) powering a telescope (12 volts) in an observatory total draw 84 watts drawn from a transformer. There is a 6...
Replies
4
Views
303
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
483
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock