You have probably read a regulation that each individual circuit must have a cpc and interpreted as each individual circuit must have its own cpc.
There is electrically nothing wrong with supplying the distribution boards using the same piece of cable.
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a seperate earth with each supply.
 
An installation can only have one earthing conductor, it is defined as being the conductor which connects the MET to the means of earthing.
The term 'main earthing conductor' does not exist in bs7671

Dave please refrain from trying to be smart and always trying to catch people out. I apologise for mister meaner. I'm sure you understood what I meant.
 
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a separate earth with each supply.
Not a problem for you to do that if you are installing it, I would think it would increase the quality of the installation in many cases and exceeding the minimum standards is generally a good thing, but it is important to be aware that it is permitted to have a single (suitably rated) cable.
 
? it would take more work to join the cable and link it than to pull it in with the tails.

same route afterall and bs7671 is a minimum standard afterall

Its an existing installation. How I would have done it in the first place is kind of irrelevant. I'm just query its suitability as a basis to make additions to the DBs.
 
Just looking in the regs to find where it says each circuit must have its own CPC and I've come across 543.1.2 in the green book (installation complete in 2011) and it clearly suggests that it is acceptable to have a common protective conductor.
 

Reply to 4 submains with one common CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K
K
Hi all, long time reader first time poster. I am an apprentice that has mainly done domestic work, but more recently we have been doing commercial...
Replies
25
Views
19K
This one might get the old grey matter going! 400A supply 260m run on ladder fed from BS88 fuses to sub main distribution board. Did a cable...
Replies
19
Views
9K
J
Hi I am having a few issues with the earthing at my house. This is a bit long winded but hopefully you can understand. I am not a time served...
Replies
37
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock