Discuss 4mm in walls is <32 yet we use 32A mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

O

ontimeelectics

I know this has been around but how is it reconciled that 4mm in plaster (with or without capping) can be used with 32A MCB when tables say cable rating is less than 32A?

Also:

I can't get my head around why a single socket spur on a single socket spur on ring is different to one double socket spur on a ring which is allowed. Surely two kettles in each arrangement would draw 26A down spur 21 cable?

Thanks.

Craig
 
The British standard for twin sockets rates them at 20A not 26A, they are not designed to handle 26A!
The test for standards compliance is a load of 13A on one side and 7A on the other.

And a kettle is only on for a couple of minutes at a time so is pretty much irrelevant to the cable rating as it is such a short term load. Electric heaters, immersion heaters or tea urns are the real problem as far as 13A sockets go.


Where have you got the idea that it is acceptable for a cable to be rated at less than the OCPD from?? This is only allowed in the case of fixed loads which by their nature are not subject to overloading.
 
4.0mm T/E ref. method C 37A table 4D7. what table are you using to get <32A?
 
4.0mm T/E ref. method C 37A table 4D7. what table are you using to get <32A?

Where is table 4D7 Tel?

Hasn't the chap got a point though? 4mm is a bit close to the 32A mark. The only time (almost) that the CCC exceeds the 32A is ref method C, so if it is enclosed in conduit on a wall or trunking it has a CCC of 30A and shouldn't be on a 32A MCB? Or if it is running above the floorboards and they have insulation in then it will have less than 32A CCC.
 
Where is table 4D7 Tel?

Hasn't the chap got a point though? 4mm is a bit close to the 32A mark. The only time (almost) that the CCC exceeds the 32A is ref method C, so if it is enclosed in conduit on a wall or trunking it has a CCC of 30A and shouldn't be on a 32A MCB? Or if it is running above the floorboards and they have insulation in then it will have less than 32A CCC.

What's wrong with being close to the 32A mark?
 
What's wrong with being close to the 32A mark?

Well nothing Dave if the CCC is a bit over, but what about if it's a bit under?

4mm is always being used as a radial on a 32A MCB so I guess I'm missing something, but if its in conduit or trunking, or has any insulation around it then its CCC will be less than 32A.
 
Last edited:
Just one last thing to the OP as I need to sleep!!

See P.320 Table 4A2 (57).. This shows that cables buried in wall are ref method C, so CCC would be 36A and fine on a 32A MCB.

As for having a single socket spurred off a single socket spur.. I can see your point about it being the same as one double spur in terms of what could actually be plugged in. But I think you have to look a bit further and think what could happen in the future, those singles could easily get changed for doubles by the next (DIY) owner.
 
Where is table 4D7 Tel?

Hasn't the chap got a point though? 4mm is a bit close to the 32A mark. The only time (almost) that the CCC exceeds the 32A is ref method C, so if it is enclosed in conduit on a wall or trunking it has a CCC of 30A and shouldn't be on a 32A MCB? Or if it is running above the floorboards and they have insulation in then it will have less than 32A CCC.

sorry. my typo. should have read table 4D5.( for flat cables), and as you say in a later post, cables in plaster, method C.
 
Personally I have never used 4mm. Even back when I worked for someone else, we always just missed 4mm out and went straight to 6mm.

Unlike 1.0mm and 1.5mm, always used 1.0mm when I first started then for some reason we changed to 1.5mm, now I don't ever seem to ask for 1.0mm, I take it that it is still readily available?
 
Personally I have never used 4mm. Even back when I worked for someone else, we always just missed 4mm out and went straight to 6mm.

Unlike 1.0mm and 1.5mm, always used 1.0mm when I first started then for some reason we changed to 1.5mm, now I don't ever seem to ask for 1.0mm, I take it that it is still readily available?

Yep still available
 
Yep it probably is wasteful. It's just another size to stock I guess that's why my last employer (my Uncle) never bothered. Not sure why one day he decided to start using 1.5mm instead of 1.0mm. Maybe it was spec on a job we did and we never changed back.
 
Yep it probably is wasteful. It's just another size to stock I guess that's why my last employer (my Uncle) never bothered. Not sure why one day he decided to start using 1.5mm instead of 1.0mm. Maybe it was spec on a job we did and we never changed back.
we use 1mm 3c sometimes usually because wholesaler hasnt got any 1.5
 
All ring and radial final circuits on our project are constructed with 4mm conductors. The vast majority of which within a metal containment system....
 
Forgot to mention, some of those 4mm final ring circuits are protected by 40A type B RCBO's.
I wonder who's going to have kittens over that, because nothing is mentioned in BS7671 or any of OSG's etc about 40A ring circuits?? lol!!
 

Reply to 4mm in walls is <32 yet we use 32A mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Guys needvadvice please I was asked to carry out an annual inspction of a DB recently There are 12 in number radial circuits suppling sockets...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock