4kwp array. 20 degree pitch. Two Strings. Data below taken on a clear sunny day, the system is under load/generating. My problem is I can't work out whether the numbers are as expected / there's an array issue as comparing with a nearby array it seems to produce less power / or I just stop worrying!

Here's a screen shot from Sunny Design:
example output.jpg

and here's the panel spec:
Pmax: 250W
Vmp: 49.08V
Imp: 5.09A
Voc: 60.36V
Isc: 5.56A
Eff: 14.7%

If I ignore VoC and ISC as I understand they are not relevant under load; and use Imp and PMax and Vmp. I also understand that these are figures under STC - and obviously this isn't "real world" - so I'd expect to see real numbers a % below.

So:

STC 1 string (panels in series) in theory is:
8*250W=2000W
8*49.08V=392V
5.09A

Where's as actual reading for string 1 is:
1696W (/250W=6.78 panels)
357V (/392=7.27 panels)
4.745A (7% drop)

This equals 7 panels. I am really "losing" a panel (and a bit) per string due to de-rating/pitch?
 
As you say, the figures on the panels are at Standard Test Conditions (STC), being a temperature of 25 degree's C, an irradiance of 1000 W/m2 and an air mass 1.5.
The figures you're seeing will likely be in conditions not equal to Standard Test Conditions so you should expect to see a difference.
 
Thanks for the replies. Perhaps I was being a bit obsessive (must get out more!) Some times comparing output with other nearby systems can be a double edged sword - you start wondering why one is "better" than the other.
 

Reply to Am I being thick? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Good Day, I Am completely new to this, if someone can verify my wiring diagram attached for the specs mentioned below please? Here are the...
Replies
0
Views
2K
D
Solar panel details Hello everyone Im a new member to the forum, i have done a course on industrial electronics so im no expert on solar panel...
Replies
2
Views
1K
Dougy
D
N
Have inspection soon and have done my install on my own house.Can someone please help with array test sheet. module is upsolar 240x7 one string...
Replies
9
Views
6K
jord35davies
J
My brain is overheating trying to make sense of PV panel parameters and calculate the CSA of a DC feed cable to the inverter. For my 16 HL Solar...
Replies
29
Views
12K
couple of questions on these, we just had a client drop these on me to install. Just reading the tech on them, im a bit unsure of the master slave...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock