Discuss Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yes the SWA is a ferromagnetic enclosure. However there is apparently going to be an exception to the requirement for CPCs to be within the ferromagnetic enclosure for SWA in the first ammendment.
 
Yes the SWA is a ferromagnetic enclosure. However there is apparently going to be an exception to the requirement for CPCs to be within the ferromagnetic enclosure for SWA in the first ammendment.

So i believe, think its due to test showing armoring spacing breaking down circulating currents
 
There is a report about from the ERA, produced for the ECA, I believe it's entitled 'ECA appendix 16' or similar.
This has information on the use of a separate CPC with SWA.
 
Just a little addition in relation to a previous point...
People coming from a 'fast track' scheme may not have covered this in enough detail to know for certain if the SWA armour is suitable for an installation - I know that I am / was unsure - This thread has helped me :)

I'm not quite sure on the point about loosing business to someone fresh (inexperienced) into the industry...
I will just state that the reason I'm here and looking for this info is because my company (not electrical) has an old boiler installation (late 80s) which I believe to be unsafe / questionable methods have been used on installations / modifications. The company has had electicians into and around the area before and no-one has commented on the installation - thus it will remain unchecked until it goes wrong. By carrying out calculations and checks, I hope to be able to get things rectified...
This kind of topic may end up generating jobs for the more experienced electrician rather than taking them away.
 
Well I have found all this a very interesting read... I for one would choose to use both the armouring and an extra core as a CPC.

I'm not quite sure on the point about loosing business to someone fresh (inexperienced) into the industry...
I will just state that the reason I'm here and looking for this info is because my company (not electrical) has an old boiler installation (late 80s) which I believe to be unsafe / questionable methods have been used on installations / modifications. The company has had electicians into and around the area before and no-one has commented on the installation - thus it will remain unchecked until it goes wrong. By carrying out calculations and checks, I hope to be able to get things rectified...
This kind of topic may end up generating jobs for the more experienced electrician rather than taking them away.

I think it is important to remember that this forum attracts people from everyday walks of life. There are some very knowledgeable and experienced people on here, there are some very knowledgeable but inexperienced people on here and there are people that have very little knowledge or experience. But we are all here for a reason, either to share our knowledge, or to gain knowledge.

YEEE HAAAAAA!
 
Nice to see this thread is still going!

I always run a run a seperate cpc (boss says so!) although its very easy to prove its not a necessity (adiabatic). good practice. He has 30 years more experience than me. I just do as i am told.............................
 
I have a similar table that the niceic sent me. Another point is that although the armouring is suitable for the circuits cpc it would be important to remember that it my not satisfy the requirements for bonding of water pipes etc if the armoured was a sub feed. Rotting of the armouring can be an issue but that is why a periodic inspection is/should be carried out to catch such issues before it completly breaks down.
 
The armour of swa should always be connected to earth and that's why you don't have to rcd protect a swa because if you damage it you will hit an earth before a live conductor, thats why you don't see a lot of two core swa about because people stopped buying it and just using the old yellow or new black as the earth. But the cross sectional area of the swa is larger than the earth conductor inside the cable, but why not connect both.
 

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
528
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Armoured cable or equivalent to go around garden border for on the ground flood lights everyone using any alternative to swa, will H07RN be OK or...
Replies
5
Views
718
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock