Discuss Difficult Service head in the UK Electrical Forum area at ElectriciansForums.net

That may be because somebody decided to turn the TT into a DIY TNCS.

But as above. It doesn't matter if you have a job to do. Unless you really know what you are doing, (and with respect, you have demonstrated that you don't) what you have done is dangerous. There's nothing between the base of that old, shaky looking service head and the substation, maybe a 600A fuse there. Instant meltdown and ambulance if you get it wrong.

I understand that I would be shaking hands with the grid should I come in contact with that. I have industrial matting and gloves for just such an occasion.

I know this looks like I've just started willy nilly taking stuff apart and yes my inexperience shows but I can assure you that it was at least conducted safely.

Thank you to everyone who has pointed that out - I won't do it again
 
What continuity reading do you get between the water bond cable in the kitchen and the consumer unit earth bar?
Daz

I've just got out the wandering lead and it's 0.02 ohms, so I'm pretty sure it's connected directly to the consumer unit earth bar.

I'm still no closer to finding how this place is earthed. I give up. I'm going to phone someone.
 
What have your Ze tests shown (with any bonding removed)?

This is the whole problem.

IF the supply is TNCS then technically I can't do the test without taking the service head apart and people get really shitty about that, apparently.

Because you shouldn't have to take the head apart - it may suggest that this is a TT system so I'm going to conduct the test from the consumer unit - in hindsight, is something I should have done right at the start. If it's a nice high reading then I would have known this was a TT system from the start.
 
Hi dude,the world won't end,and we have all done madder things...just don't talk about it,and provide pictures.
The original information you seek,may have been found with a phone call.

What type of property is it?

Do some deleting,have a think,and come back to us.
 
That 10mm or 16mm green /yellow is probably your earthing conductor from the cut out to your consumer unit
You can verify with a continuity test
At the consumer unit you may then find some bonding cables for services

At the consumer unit disconnect the earthing conductor and measure Ze,if the reading is within the 0.35 it may likely be Tnc-s,however,only the supplier can verify that it is indeed Tnc-s and we have to rely on a Pme sticker telling us or to ask them
They have an obligation to inform you of the type of earthing that they may or may not provide
 
To add my measly morsel, that service head would 'appear' to bear the resemblance of a PME supply, with a very poorly terminated neutral, normally covered in a nice black plastic boot not a black plastic box?

I also see the main fuse, and the detachable cover to the service head neutral. Worryingly, there doesn't seem to be an earthing conductor connected into the service head neutral (OP suggests the one in the picture is connected to gas service pipe?), which suggest it's missing or it's not a PME supply. Phone to the DNO in that case, to clarify (unless you find an earth rod somewhere!), and perhaps they might have a view on their service cable termination?

As an aside, removal of DNO seals (please no Pinnipeds jokes :)), varies by different DNO. Mine SSEN, allow electricians in government approved schemes, to remove seals where necessary, remove main fuse, to carry out work on customers tails. Replace main fuse, put on SSEN temporary seal and ring them with details. Check with your DNO to find their policy on seal removal.

View attachment 35664

View attachment 35663
 
This is the whole problem.

IF the supply is TNCS then technically I can't do the test without taking the service head apart and people get really shitty about that, apparently.

No mate, you disconnect at the MET (within the Consumer Unit) if that's all you can do (I say that as some modern heads have holes in the head for test probes).

If it's a high reading it'll probably be TT. If it's a low Ze reading, it could be TNCS - one way to affirm more (apart from phoning DNO) is to then carry out a Zl. If Zl is the same reading as Ze, then there's a good chance it's TNCS.
 
Ok to confuse things more the Ze test is 0.11 ohms - it is not TT.

That earth you can see is 100% definitely the gas pipe bond.
 
Hello all,

I've recently put a new circuit in a house and when filling out my EIC, I needed to access the service head (attached).

I'm relatively new to this and I'm struggling here.

In order to access ANY part of this, you have to pull the main fuse and I had to cut a few metal tallys off. As you can see on the left is where the main fuse sits, to the right there is a cover for the MET and underneath is a cover for the incoming cables. The black box between the meter and thefuse housing is not removable - I can't see where the main earth is. The earth cable you can see is bonding from the gas pipe.

Also, immediately I thought it was a TNS system but it gets quite strange. The what looks like SWA is not SWA, it looks and feels like copper!! IT DEFINITELY isn't steel. Additionally, I can't find a neutral anywhere, I can't see if it is in with the red incoming wire but I'd be pretty surprised if it was.

Could the copper SWA (I know) actually be the PME neutral and we are actually looking at a TNCS system here?

Either way, I have never seen anything like this cable before.

Thanks in advance, I genuinely don't know if I'm just being stupid or inexperienced here but I'm kinda stuck with a way ahead.

View attachment 35655

View attachment 35656

View attachment 35657
Put it all back together, clean your finger print and any DNA from the area, claim you had amnesia if anyone says anything, you shouldn't be frolicking about inside the head it's not yours to play with.
 
Put it all back together, clean your finger print and any DNA from the area, claim you had amnesia if anyone says anything, you shouldn't be frolicking about inside the head it's not yours to play with.

Thanks for the advice but believe me, I have been told enough.
 
Ok to confuse things more the Ze test is If that is a Gas bond, how did you measure Ze without verifying the earthing conductor 0.11 ohms - it is not TT.

That earth you can see is 100% definitely the gas pipe bond.

If that is a Gas bond, how did you measure Ze without verifying the earthing conductor
 
OP, as already advised by members, think you just need to go back to basics, and verify earthing conductor and main bonding conductors, just in case you've made a mistake. We are all human.
 
OP, as already advised by members, think you just need to go back to basics, and verify earthing conductor and main bonding conductors, just in case you've made a mistake. We are all human.

Yep, I'm going to start again, this is turning into a mess.
Thanks for all the advice everyone.
 

Reply to Difficult Service head in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I'm shadowing the electrician who is doing our EICR's and after visually inspecting the service cable and service head, I noticed a bit...
Replies
12
Views
1K
I had a look at a property with this old service head. It's a looped supply, the met is just a bolt and the tn-s earth is questionable. There's...
Replies
13
Views
3K
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
325
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock