Just a thought,

G83 over freq setting maybe in the range of G59 setting but it is also a full 1Hz below the reccomended limit. So nuisance tripping on larger systems might cause problems with the dno, thats why G59 settings are more forgiving. It does'nt explain why only the frequency limit has to be altered and not the rest of the parameters.
 
I think you may be right there. Here is a G59 extract:

Capture.JPG

and also explains perhaps why sma went to the trouble of certifying their tripower range to the g59 standard in Feb this year

Regards
Bruce
 
Last edited:
I was in contact with SMA to query aspects of the 4000TL, and specifically to see if it could be restricted to 16A output. I have copied below a reply I received asking if G59/2 certification would be useful? As a consumer, and having now completed my install, it's clearly of no concern to me but you might like to voice your opinion to the contact details below if you feel that certification would be helpful.

Dear Mr. S....,

currently we are discussing, if it is more usefull to have the G59/2 certificate for all inverters with a AC-current > 16 A. As I understand the regulations it is possible to use Generating Units > 16 A per phase and ≤ 50 KW 3 phase which must be G59/2 compliant. A type verified protection equipment is accepted.
So, would it be more helpful that you have the G59/2 certificate for that inverter ?


mit freundlichen Grüßen
Yours sincerely
SMA Solar Technology AG
i. A. Bernd Krah

Technical Support Medium Power Solutions
Sonnenallee 1
34266 Niestetal
Germany
Tel.: +49 561 9522-3314
Mobil: +49 151 54345943
Fax +49 561 9522-4080
E-mail: [email protected]
 
Last edited by a moderator:
I had a chat with a chap from CE Electric, at the Yorkshire and Humber Microgeneration Project conference yesterday, and he confirmed they use the inverter output for the rating.

I also got it in writing.
 
bit of confusion lately from board to board
some allow 16amp plus , some stick are rigid at 16amps output
two options
decrease dc Kwp of the system to approx 3.68kwp one less panel or 5/10wp decrease per panel
fit new 2011 sma sunny boys with limited 16amps output , bit of a waste of clients dc kwp output on sunny days
16amps on three phase generally not a problem eg with sma 10kwp STP10,000TL inverters

never had a answer from a dno yet about the answer if you fit a 4kwp dual-axis tracker
increase output by 30-45% compared to fixed systems
with high yield solarworld/sanyo with high effciency sma TL inverter
 
fit new 2011 sma sunny boys with limited 16amps output

Looking at the current spec sheets where can I find that?

I have a west facing roof which we are looking at using the SMA SB3800 on, and I am looking for the maximum rating so that we can do it without needing to do a pre-install application. (3.68 kw) Only other inverter I can find maximum continuous rated at 16A / 3.68kW is the Diehl Ako 4300S
 

Reply to DNOs and G83 limit in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I'm not an electrician, just a householder (though do work in an area given a kick in the family jewels by government decision last year). I am...
Replies
12
Views
3K
S
We have a customer with an interesting problem! Proposed install is on a split phase supply @ 460V 50kW system with existing DNO permission - As...
Replies
3
Views
1K
S
What implications are there from underspecifying an inverter? (1) What actually results at the inverter, should the irradiance on the panels...
Replies
18
Views
3K
D
Hi, Just contacted SP energy networks re. a 4kWp installation to see what my options are and was told definitely only G59. However, I see from...
Replies
3
Views
3K
JulianC
J
We've received a note from WPD with an application which has been approved in South Wales which is out of our usual area although same DNO...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock