Discuss duplicate protective conductor question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Is there a requirement stipulating a final circuit supplying only one socket outlet should incorporate a duplicate protective conductor?

Not solely for the reason that there is single outlet, but it may be required of the equipment the socket is intended for has an expected earth leakage greater than 10mA
 
Would there ever be a need for a high-integrity CPC outside of a special location, for one double 13A? The maximum leakage current of an appliance connected via a BS1363 plug is 3.5mA, so 7mA total. It's possible that multiple high-leakage, low load appliances might be connected with multiway adaptors but in a domestic installation the probablility is negligible and not foreseeable in design. In a commercial or industrial one, it could be foreseen but an alternative socket outlet would then be specified e.g. CEE17 feeding a local PDU.
 
There no problem with it, what prompted me to ask is that I was suspicious that it had been incorrectly installed.
If there were two sockets therefore radial circuit a duplicate protective conducter would be incorporated but I wasn't sure if that was the case for one socket.
 
If there were two sockets therefore radial circuit a duplicate protective conducter would be incorporated
Not sure what you mean. A normal radial circuit has only one CPC no matter how many points it serves.
 
That's not a normal radial circuit. The duplicate conductor would only be installed for a circuit with design functional earth leakage >10mA, typically in an industrial or commercial application with large quantities of IT equipment.
 
Out of interest, do you normally run a second cpc on your radial circuits then?
 

Reply to duplicate protective conductor question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
664
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510
Question about the Definition of #6 wiring standards for Thailand as of 2023? I am having a House/Villa built in Thailand and I wanted to wire...
Replies
0
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock