Discuss EICR 3036 board - coding - meter tails in the UK Electrical Forum area at ElectriciansForums.net

I always put the DNO fuse as "Not Verified" on an EICR. What make is the board some of the Wylex boards are of wood frame construction. So where and why are you practising this on?
 
Maybe you should have supplied more information initially. The amount of people who come on here asking what side to butter their bread on is unbelievable.
One question, how have you decided none of the sockets will supply equipment out of doors, check in the shed for a lawnmower :)
Whichever side you do decide it still ends up butter side down when you drop it.
Sods law
 
Im not doing the actual EICR, Ive just done it for practise.

But am I sure whether I should be doing EICRs, with enough experience, yes. But I didn't come here to discuss my competency with yourself, I came here for advice.

type of supply TN-S
Fuse type BS88 GG 100A
small two bed cottage
No sockets to supply outside equipment

Any thoughts would be appreciated.
Have you verified the characteristics of the protective device? If not, how can you code the tails.

I wouldn't code the CU.

Why are you coding the lack of RCD protection as C2?
 
Since when it was installed it was up code unless the install has become dangerous since then would it be c3 with an advisory? Or no code?
Still an apprentice so don't do eicrs just curious.
 
Ok Lumie, you have ( unintentionally ) poked a hornet's nest with a big stick.
It would have been helpful if, as part of your OP, you had explained this was a hypothetical question, that you don't carry out EICRs and that you are just trying to get your head round how certain things might be coded....then some of the responses might have been more moderate.

No harm in asking questions, that's hopefully one of the ways we all learn, but you must explain the context of your question.
Now, you probably have the answers you were looking for..
- a CU with rewireable fuses will not necessarily attract any code ( hardwood or plastic), but it may do.
- no rcd protection may not attract any code, but it could also be a 3 or 2 depending upon the particular situation.
- 16mm tails on a 100A BS88/1361 may only receive a comment if the max demand is lower that the ccc of the tails.

What you will have learned is that coding will depend on several/many specific factors and you need to be aware of them all, as well as the specific regs you believe are being broken, before you start allocating codes. And to do EICRs professionally, you must have an above average understanding of BS7671!
 
Fair comment on the reg number, do you do that for every code?

Its a plastic board. Not quite sure what you mean by the wooden boards being damn near incombustible, when wood is very combustable?

The loading on the tails is minimal.

Just from the sticker on the cut out fuse. How else can you prove it? Im not contacting the DNO as this is just for practise.

Thanks for the help

Yes of course you quote regs, you can't code things that aren't in the regs.

The wood is treated to be fire retardent, just try getting it to burn!
The plastic used in those days wasn't particularly combustible.
 
Which regulation mentions the location of the CU being a deciding factor?
Comes form the NICEIC examples of codes.
I sought guidance as to what to code this if any from an area inspector.
If the db is in an area of sole means of escape but has no signs of thermal damage or loose connections c3.
Now you can argue with this statement all you like but I do see where it comes from.
As bs 7671 calls for non combustible materials to be used or a cu to be installed in a non combustible enclosure, I don't think it's unreasonable to c3 it in an escape route of a dwelling.
Final coding is down to the inspector as the buck will stop with him.
As you know a c3 is still a satisfactory outcome just an improvement of the overall safety and nothing more.
 
Comes form the NICEIC examples of codes.
I sought guidance as to what to code this if any from an area inspector.
If the db is in an area of sole means of escape but has no signs of thermal damage or loose connections c3.
Now you can argue with this statement all you like but I do see where it comes from.
As bs 7671 calls for non combustible materials to be used or a cu to be installed in a non combustible enclosure, I don't think it's unreasonable to c3 it in an escape route of a dwelling.
Final coding is down to the inspector as the buck will stop with him.
As you know a c3 is still a satisfactory outcome just an improvement of the overall safety and nothing more.

the regulations make no mention of the location of the CU so the code, if any, must be the same regardless of location.
 
the regulations make no mention of the location of the CU so the code, if any, must be the same regardless of location.
No they don't , however if a fire is to start in a plastic consumer unit and is in the vicinity of the sole means of escape of the dwelling then it's a dangerous situation. Obviously the db should be checked for loose connections during the eicr for possible c1/ c2 codes.
The non combustible regulation came in to contain a possible fire if one was to occur.
Just my take on it Dave.
 
No they don't , however if a fire is to start in a plastic consumer unit and is in the vicinity of the sole means of escape of the dwelling then it's a dangerous situation. Obviously the db should be checked for loose connections during the eicr for possible c1/ c2 codes.
The non combustible regulation came in to contain a possible fire if one was to occur.
Just my take on it Dave.

If fire starts in a consumer unit it is a dangerous situation wherever the CU is located. Especially considering the common habit of people to bury it under all manner of junk, coats etc.
If fire starts in a metal CU which has flammable materials touching it then you can pretty much guarantee that those materials will catch fire.

Not to contain a fire, just to not combust, very different things. CUs are not fire rated to withstand fire for any length of time, thin sheet steel is not suitable for such an application on its own
 
If fire starts in a consumer unit it is a dangerous situation wherever the CU is located. Especially considering the common habit of people to bury it under all manner of junk, coats etc.
If fire starts in a metal CU which has flammable materials touching it then you can pretty much guarantee that those materials will catch fire.

Not to contain a fire, just to not combust, very different things. CUs are not fire rated to withstand fire for any length of time, thin sheet steel is not suitable for such an application on its own
It will contain it longer than plastic.
That's why it's changed or you might as well leave it as plastic.
 
To add to the debate. I was under the assumption, that the idea behind A3 non combustible materials, was to remove a potential fuel source from a potential ignition source. Nothing to do with containment.
 
on the AMD3 fuse boards - we HAVE to remember that its a simply metal enclosure around the dodgy poor quality parts produced by BEAMA...
 
Although when the reg 421.1.201 came into being, a lot was made of containment. This philosophy, quickly changed when everyone started bumping their gums about intumescent sealing and the fact that a standard A3 CU, has a huge flaw in containment, with a largely flappy poorly sealing lid. :)

So, as I've since heard and read, its about removing the rather doubtful inflammable plastic, with something else, mostly it seems ferrous metal.
 
Be nice if people could carry out EICRs using gained knowledge and competence as opposed to harping on about the Best Practice Guide and what the NICEIC make up, well we would certainly have less people doing them that is for sure.
 

Reply to EICR 3036 board - coding - meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
645
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
407
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
534
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock